Transformer Overcurrent Protection Explained
Transformer overcurrent protection is required to protect the primary windings from short circuits and overloads and the .secondary windings from overloads. Section 450.3 of the National Electrical Code (NEC) contains the requirements for overload protection of transformers. Overcurrent protection requirements depend on the following factors:
- The voltage at which the transformer operates. Section 450.3 (A) of the Code contains the rules for transformers rated over 600 V, nominal. Section 450.3 (B) contains the rules for transformers operating at 600 V. nominal or less.
- Location of the overcurrent device. Requirements vary depending on whether only the primary winding is protected or both the primary and secondary windings are protected.
- For transformers rated over 600 V only, the conditions of maintenance. If conditions of maintenance ensure that only qualified personnel will work on the transformers, Table 450.3 (A) permits primary protection only for these supervised installations.
- For transformers rated over 600 V, when both primary and secondary protection is provided, the impedance of the transformer is considered.
- When ,both primary and secondary protection is provided, overcurrent protection requirements vary based on whether or not the transformer is equipped with a coordinated thermal overload protection by the manufacturer.
Power System Protection Courses
Short Circuit Study & Protective Device Coordination
Arc Flash Analysis/Study - IEEE 1584 Update
Rules for sizing overcurrent protection for a transformer operating at more than 600 volts are covered in Section 450.3(A) and Table 450.3(A) of the NEC. When only primary protection is provided in a supervised location, the maximum current rating of the fuse is 250% of the full-load current (FLA) of the primary. If a circuit breaker is used for protection, the maximum size is limited to 300% of the full-load primary current. In both cases, when the calculated current value is not equal to a standard size of fuse or circuit breaker the next larger size may be used.
Rules for sizing overcurrent protection for a transformer operating at 600 volts or less are covered in Section 450.3(B) and Table 450.3(B) of the Code. Where only primary protection is provided, the general rule is that the fuse or circuit breaker shall not exceed 125% of the full-load primary current.
For transformers 600 volts and less, the overcurrent device protecting the primary of a transformer is permitted to be rated as large as 250% (or the next smaller size) of the primary full-load current, provided the transformer secondary winding is protected. The transformer secondary over-current device rating is not permitted to be greater than 125% (or the next larger size) of the secondary full-load current.
Transformer overcurrents, like that of other devices, may be classified as being due to overloads or short circuits. A transformer overload condition is said to exist when it is delivering from one to six times its normal current rating. In this case the current is confined to its normal path and a temperature rise takes place in the transformer.
When a transformer short circuit condition exists, current is not confined to the normal wiring channels to the load. Short circuit currents can reach levels that are hundreds of times greater than the normal full load operating current. Damage can be extensive if protective devices do not react in milliseconds to open the current path created. As discussed previously, the impedance rating of the transformer is used to calculate short circuit current and to determine the interrupting current capacity required by the protective device.
Read Other Electrical System Protection Articles
Transformer Protection Explained
Maximum Fault Current Calculation