How to Calculate Arc Flash Incident Energy

How to Calculate Arc Flash Incident Energy

There are two basic standards that establish requirements for AF hazards. The first is NFPA 70E, Standard for Electrical Safety in the Workplace, which defines the basic practices to be followed for electrical safety, including personal protective equipment ppe levels which must be worn for given levels of arc flash incident energy and what steps must be taken prior to live work on electrical equipment. The second is the IEEE Guide for Performing Arc-Flash Hazard Calculations, IEEE 1584-2018 which gives the engineer the methods for calculating the severity of arc flash incident energy levels.

 

Visit our Arc Flash Study/Analysis Course

www.electricityforum.com/electrical-training/arc-flash-analysis-training

 

How to Calculate Arc Flash Incident Energy

In electrical systems, an AF can release dangerous amounts of energy, posing serious risks to personnel working nearby. To minimize these risks, performing an arc flash analysis is essential for assessing the potential energy and ensuring that workers are adequately protected. Calculating the arc flash incident energy is a critical step in determining the required personal protective equipment (PPE), defining safety boundaries, and minimizing the hazards of working on live electrical systems.

 

What is Arc Flash Incident Energy, and Why is It Important to Calculate It?

Arc flash incident energy refers to the amount of thermal energy, measured in calories per square centimeter (cal/cm²), that a worker may be exposed to during an AF event. This energy can cause serious burns, even at relatively low levels. Calculating this energy is essential for understanding the risk level in an electrical environment and determining the appropriate PPE for workers to prevent injury. The calculation is also key in establishing the AF  boundary, which defines the distance from the electrical equipment where PPE is required.

By determining the arc flash incident energy, companies can comply with standards like NFPA 70E and IEEE 1584, safeguarding workers and minimizing the risk of catastrophic injury.

 

What Formulas or Methods Are Used to Calculate Arc Flash Incident Energy?

There are two primary methods for calculating incident energy:

  • The IEEE 1584 Method: This is the most widely used approach for conducting an analysis. IEEE 1584-2018 offers updated guidelines for more accurate calculations based on extensive testing in various conditions. The method accounts for factors such as bolted fault current, arcing time, and system configuration. The calculations are complex but provide accurate results for different equipment types and electrical configurations.

  • The Lee Method: This method, developed by Ralph Lee, is a simplified calculation for estimating incident energy in open air AF scenarios. It’s suitable for high-voltage systems and uses basic assumptions, but its simplicity makes it less accurate than the IEEE 1584 method. It’s often used as a quick reference or when detailed system data is unavailable.

Both methods are detailed in the guide for performing AFhazard calculations, providing step-by-step instructions to ensure accurate and reliable results.

 

What Input Parameters Are Needed to Calculate Arc Flash Incident Energy?

To perform an analysis, several input parameters are required to determine the incident energy accurately. These parameters include:

  • System voltage: The higher the system voltage, the greater the potential for a severe AF event.
  • Fault current: This is the maximum current that can flow during a fault condition, including a bolted fault or short circuits. Higher fault currents lead to higher energy release during an electrical explosion.
  • Arcing time: This is the duration of the AF, typically determined by how quickly a protective device, such as a circuit breaker, interrupts the fault. Shorter arcing times reduce the energy released.
  • Working distance: This is the distance from the arc to the worker’s body. A greater working distance reduces the energy exposure and the severity of the injury.
  • Equipment configuration: The size, type, and arrangement of electrical components also influence the calculation, as does whether the event occurs in open air or within an enclosure.

These parameters are critical in accurately estimating the arc flash incident energy and establishing safe work practices.

 

How Does the Working Distance Affect the Calculated Arc Flash Incident Energy?

The working distance — the space between the worker and the source of the arc — is a significant factor in determining the severity of the energy exposure. As the distance from the arc increases, the energy diminishes rapidly. This reduction is due to the inverse square law, where energy dissipates over distance. For example, doubling the distance from the arc can reduce the energy exposure by a factor of four.

This makes it crucial to factor in the working distance when conducting an analysis. Ensuring that workers maintain a safe distance from energized components, or using remote operating tools, can significantly reduce the risk of injury from an AF event.

 

What Tools or Software Are Available to Help Calculate Arc Flash Incident Energy?

Given the complexity of arc flash calculations, specialized software tools and AF calculators are often used to streamline the process and ensure accuracy. These tools take into account all the necessary input parameters, including system voltage, fault current, arcing time, and equipment configuration, to provide reliable estimates of incident energy.

These programs are built to comply with IEEE 1584-2018 and NFPA 70E, ensuring that the results meet industry standards. Additionally, they can simulate different electrical scenarios, making them invaluable for risk assessment and planning.

Calculating arc flash incident energy is an essential part of protecting workers from the hazards of AF events. The process involves multiple steps, starting with inputting critical parameters such as fault current, arcing time, and working distance. Utilizing accurate formulas like those provided in IEEE 1584-2018, combined with modern AF calculators, allows for precise and reliable results.

Understanding the importance of distance from the arc, using protective devices such as circuit breakers, and following guidelines set out by NFPA 70E are crucial for ensuring a safe work environment. With the proper tools, including software designed for analysis, organizations can confidently protect their workers and comply with electrical safety standards.

By implementing these practices and understanding the variables involved, businesses can reduce the risks of AF events and create safer electrical systems.