Latest Generators/UPS Articles
Automatic Transfer Switch
An automatic transfer switch (ATS) seamlessly shifts electrical load from the utility to a backup generator during power outages. It ensures continuous power, improves safety, and protects sensitive equipment from unexpected power loss or fluctuations.
What is an Automatic Transfer Switch?
An automatic transfer switch (ATS) is invaluable for maintaining a reliable power supply in unpredictable outages. It:
✅ Automatically switches power from utility to generator during outages
✅ Enhances safety and prevents electrical backfeed
✅ Protects equipment by ensuring uninterrupted power flow
Emergency Generator Standby Power Training
Power Quality Analysis Training
Request a Free Emergency Generator Training Quotation
Technical Depth: Controllers and Monitoring Logic
Modern automatic transfer switches rely on intelligent control systems to ensure seamless and safe operation during power outages. These controllers are the "brains" of the automatic transfer switch, constantly monitoring utility and generator power for any abnormalities such as voltage drops, frequency fluctuations, or phase loss. By using microprocessor-based technology, the ATS can make precise decisions and execute transfers with minimal delay.
Modern ATS use advanced microprocessor-based controllers that continuously monitor utility power for voltage, frequency, and phase stability. These controllers initiate a transfer only when they detect abnormal conditions, preventing unnecessary switching. Features such as time-delay settings, load testing, event logging, and communication interfaces for remote monitoring enhance reliability and operational control, particularly for facilities with sensitive equipment. For a deeper look into reliable backup power solutions, check out our section on emergency backup generators.
ATS Types and Transition Mechanics
ATSs are designed to handle different power transfer needs depending on the criticality of the load and the application. The transition method determines how the automatic transfer switch switches from the utility power to the backup generator and back again. Each type of transition offers unique advantages in terms of reliability, smoothness of power delivery, and equipment protection.
There are three primary transition types in automatic transfer switches:
-
Open Transition (Break-Before-Make): Disconnects the load from the utility before connecting to the generator. This avoids overlap and is commonly used in residential and standard commercial systems.
-
Closed Transition (Make-Before-Break): Briefly connects both power sources during transfer, minimizing interruptions. Ideal for hospitals and critical facilities.
-
Delayed Transition: Adds a pause between transfers to allow motor loads or residual currents to discharge, reducing equipment wear and electrical stress.
Choosing the right transition type depends on load sensitivity and operational requirements.
Automatic Transfer Switch Key Details
| Feature | Description | Applications/Benefits |
|---|---|---|
| Controller Technology | Microprocessor-based controllers monitor voltage, frequency, and phase stability to trigger smooth transfers. | Prevents false transfers, supports remote monitoring, improves reliability. |
| Open Transition | Break-before-make operation disconnects utility power before connecting to the generator. | Standard residential and commercial systems. |
| Closed Transition | Make-before-break operation allows brief overlap between power sources. | Hospitals, data centers, and critical operations where no power interruption is acceptable. |
| Delayed Transition | Introduces a pause between power sources to dissipate residual energy from motors or inductive loads. | Industrial facilities with heavy motor loads. |
| Generator Sizing | ATS must be rated to handle generator output and inrush currents. | Prevents overloads and ensures stable power transfer. |
| NEMA Enclosures | Protects ATS components based on environment (NEMA 1 indoor, NEMA 3R/4 outdoor). | Ensures durability and compliance with installation standards. |
| Load Management Features | Includes load shedding or prioritization for critical circuits when generator capacity is limited. | Maximizes backup power efficiency. |
| Amperage Ratings | ATS must match service amperage (residential, commercial, or industrial). | Guarantees safe and effective operation. |
Selection Criteria for an ATS
Selecting the correct ATS requires a careful evaluation of the power needs, system design, and environmental factors. The right ATS ensures that the generator and connected loads operate safely and efficiently during an outage. Factors such as load priorities, installation environment, and power quality features can significantly impact performance and reliability.
When selecting an automatic transfer switch, consider:
-
Generator Sizing: The ATS must match the generator’s maximum output, taking into account surge loads and starting currents.
-
NEMA Enclosure Types: Use NEMA 1 for indoor environments, NEMA 3R or 4 for outdoor or harsh conditions.
-
Load Management Features: Some ATS models provide load shedding or prioritization to manage generator capacity.
-
Amperage Ratings: Match the switch to your total service amperage for safe operation in residential, commercial, or industrial settings.
Learn how different battery backup systems work to keep critical loads powered during outages.
By selecting the right switch, ensuring correct installation and maintenance, and adhering to safety best practices, you can enjoy the benefits of a backup power system and the peace of mind it provides.
Power outages
Power outages can cause significant disruptions to our daily lives and business operations. Ensuring a consistent and uninterrupted power supply is crucial in today's world, which relies heavily on technology and electricity. An ATS is a reliable solution for maintaining power during outages.
An automatic transfer switch is an essential component of any backup power system. It facilitates seamless power transfer between the primary power source and a standby generator during an outage. By doing so, the ATS helps maintain a continuous flow of electricity, safeguarding homes and businesses from the negative impacts of power loss.
When selecting an appropriate automatic transfer switch, factors such as generator power capacity, load type, and intended application are crucial. Consulting with an electrical switchgear expert is a wise step in making an informed decision. Consider the voltage and amperage ratings, as well as the intended use of the switch, whether for residential, commercial, or industrial purposes. Switchgear systems may offer various features, such as remote monitoring and built-in diagnostics, catering to different requirements. Our article on emergency power supply explains how these systems provide seamless transitions during utility failures.
Automatic transfer switches and manual transfer switches
Automatic transfer switches and manual transfer switches differ in their operational modes. While a manual transfer switch necessitates physical engagement by an individual to shift the load between the main power source and the backup generator, an ATS performs this task automatically, ensuring a more efficient and dependable response.
Proper installation and maintenance of an ATS are crucial for its optimal performance and longevity. Although a qualified electrician should always perform installation, end-users can perform basic maintenance tasks, such as routine inspections, cleaning, and testing. Specialized servicing should be left to professionals to ensure the ATS remains in peak condition.
The main components of an ATS include the transfer switch, a controller, and a power source. The transfer switch, either open transition or closed transition, connects and disconnects the load between the utility power and the standby generator. The controller monitors voltage levels and initiates the load transfer when required. Finally, the power source, typically a backup generator, supplies power during an outage.
An ATS is vital for ensuring an uninterrupted power supply during an outage. First, it detects a power outage and signals the standby generator to start. Once the generator runs, the ATS conducts a load transfer from the primary power source to the backup power system. After power is restored, the ATS switches the load back to the utility power and shuts down the generator. This smooth process minimizes the detrimental effects of power outages.
Automatic Transfer Switch In Critical Facilities
Critical facilities, such as hospitals and data centers, require a bypass isolation switch for added redundancy and maintenance flexibility. The bypass isolation switch enables the ATS to be serviced or replaced without interrupting power to the facility.
Single-phase and three-phase automatic transfer switches are the two primary types, with their usage varying according to application and load requirements. Single-phase switches are commonly used in residential settings, whereas three-phase switches are typically employed in commercial and industrial applications.
Safety should always be a top priority when working with an ATS. Please ensure that a licensed electrician installs the switch and follows the manufacturer's guidelines for maintenance and testing. Additionally, appropriate personal protective equipment should be used when handling electrical switchgear, and all applicable local and national electrical codes should be followed.
Frequently Asked Questions
What is an ATS?
An ATS is an electrical device that automatically transfers power from the utility to a backup generator when an outage occurs, ensuring uninterrupted power.
How does an ATS work?
An ATS continuously monitors incoming utility power. If it detects a failure, it triggers the generator to start and shifts the electrical load. When utility power returns, it smoothly switches back.
Which ATS is best for home or commercial use?
Homes typically use single-phase ATS units with lower amperage, while commercial or industrial facilities require three-phase models designed for larger loads and critical operations.
Related Articles
Sign Up for Electricity Forum’s Generators/UPS Newsletter
Stay informed with our FREE Generators/UPS Newsletter — get the latest news, breakthrough technologies, and expert insights, delivered straight to your inbox.
DC Generator Explained
A DC generator converts mechanical energy into direct current electricity for use in backup power systems, industrial machines, and battery charging. It provides reliable, consistent DC power output for various electrical and energy conversion applications.
What is a DC Generator?
A DC generator is an electromechanical device that produces direct current by converting mechanical energy.
✅ Converts mechanical energy into direct current electricity
✅ Used in battery charging, backup power, and industrial systems
✅ Delivers consistent voltage for energy conversion and power supply
Emergency Generator Standby Power Training
Power Quality Analysis Training
Request a Free Emergency Generator Training Quotation
A DC generator is vital in converting mechanical energy into electrical energy. By employing the principles of electromagnetic induction, this versatile machine has powered various applications across industries. However, as technology advances, understanding its fundamental workings, types, and maintenance remains crucial for professionals and enthusiasts alike. Our article on emergency power supply explains how these systems provide seamless transitions during utility failures.
In today's world of rapidly evolving technology, one often comes across devices that can convert mechanical energy into electricity. One such device is the DC generator, which has existed for over a century. As a fundamental part of the electrical industry, DC generators have powered countless applications, including small-scale electronics, vehicles, and large industrial machines. Our guide on emergency backup generators explains how these systems keep critical loads running during outages.
Electromagnetic Induction: The Principle Behind DC Power Generation
To understand the workings of a DC generator, we must first explore the concept of electromagnetic induction. This phenomenon, discovered by Michael Faraday in the early 19th century, states that a voltage, or electromotive force (EMF), can be induced in a conductor when it is exposed to a changing magnetic field. This induced EMF drives the flow of electric current, producing electricity. DC generators rely on this principle to generate Direct Current. For a broader overview of how engines operate, explore our article on how a generator works.
Key Components
The primary components are the stator, rotor, armature, field winding, commutator, and brushes. The stator houses the stationary magnetic field, which can be generated by permanent magnets or field coils. The rotor, on the other hand, contains the armature windings where the EMF is induced. As the rotor rotates within the magnetic field, voltage is generated in the armature windings through electromagnetic induction.
How a Commutator Converts AC to DC
The commutator, a crucial component, is responsible for converting the alternating current (AC) produced in the armature windings into Direct Current. It continuously changes the connections between the armature windings and the external circuit, ensuring the current flows in one direction. In addition, brushes maintain contact with the commutator, transferring the generated electricity to the external circuit.
DC Generator vs. AC Generator: What’s the Difference?
A DC generator produces a direct current, which flows in a single, constant direction. In a DC generator, a commutator ensures that the current generated in the armature windings always flows in the same direction. This is achieved by continuously changing the connections between the armature windings and the external circuit. As a result, the output voltage and current remain constant in polarity. They are used in applications requiring a stable voltage supply, such as charging batteries, powering small electronic devices, or operating DC motors.
An AC generator, an alternator, produces an alternating current that periodically reverses direction. AC generators do not require a commutator, as the output current can change direction naturally due to the rotation of the armature within the magnetic field. The output voltage and current follow a sinusoidal waveform, meaning they vary in magnitude and direction over time. AC generators are more commonly used than DC generators, as AC power can be easily transformed to different voltage levels and is more efficient for long-distance transmission. Most power grids and household electricity supplies rely on AC power.
The main difference between it and an AC generator is the type of electrical current they generate. They produce a constant unidirectional current, while AC generators produce a sinusoidal current that reverses direction periodically. Both types have their specific applications and advantages, depending on the requirements of the electrical system they are used in. Learn how different battery backup systems work to keep critical loads powered during outages.
Types and Their Applications
Several types of DC generators exist, including series-wound, shunt-wound, and compound-wound devices. These classifications are based on how the field winding is connected to the armature winding. Each type has its unique characteristics, making it suitable for specific applications.
Series-wound units have the armature and field windings connected in series. They provide high current but relatively low voltage output, making them suitable for starting large motors or powering arc welding machines. In contrast, shunt-wound types have their field windings connected in parallel with the armature, providing a more stable output voltage suitable for battery charging and lighting systems. Finally, compound-wound types have both series and shunt windings, offering the advantages of both types and finding use in applications requiring stable output voltage with varying loads. Discover how an automatic transfer switch ensures seamless transitions between utility and electrical power.
Voltage Regulation and Efficiency
The output voltage can be regulated through various means, such as adjusting the field current, employing voltage regulators, or using feedback systems. These methods ensure the generated voltage remains stable, even under varying load conditions, safeguarding the connected devices from damage due to voltage fluctuations. Interested in long-term performance? Learn how long battery backups last and what factors affect their reliability.
DC Generator Maintenance and Troubleshooting Tips
Proper maintenance and troubleshooting are essential for its long-lasting operation. Regular inspection of brushes, bearings, and other components, as well as lubrication and cleaning, is necessary to prevent premature wear and tear. Additionally, any performance irregularities should be promptly addressed by assessing the output voltage, load resistance, and other factors to identify and rectify the underlying issues. For a deeper look into reliable backup power solutions, check out our section on emergency backup generators.
Related Articles
What is a UPS System?
A UPS system (Uninterruptible Power Supply) provides backup power during outages, protects equipment from voltage fluctuations, and ensures the continuous operation of critical systems in data centers, hospitals, and industrial facilities.
What is a UPS System?
It is a vital resource for businesses that need backup power to maintain operations during a power outage or other interruptions that could lead to significant financial losses.
✅ Provides immediate backup power to prevent system shutdowns
✅ Improves power quality with surge protection and voltage regulation
✅ Protects servers, networks, and critical loads with monitored battery runtime
Emergency Generators and Standby Power Training
Request a Free Training Quotation
It offers power protection, backup supply, conditioning, surge protection, management, and emergency power supply. In this article, we will explore the various types of UPS and explain in detail how a UPS works using the keywords you provided. For a broader overview of backup solutions and related technologies, visit our section on Electrical Generators and UPS Systems.
Types of UPS Systems
Three main types of UPS systems exist: online double conversion, line-interactive, and standby. Let's explore each of these types and their unique features and benefits. To understand how UPS units integrate with switching equipment, see our article on the role of an Automatic Transfer Switch in emergency power continuity.
Comparison of UPS System Types: Features, Performance, and Applications
| Feature | Online Double Conversion UPS | Line-Interactive UPS | Standby UPS |
|---|---|---|---|
| Power Protection Level | Highest | Moderate | Basic |
| Transfer Time | 0 ms (no delay) | 2–4 ms | Up to 10 ms |
| Power Conversion | AC ➝ DC ➝ AC (full double conversion) | AC with voltage regulation | Switches from utility to battery |
| Voltage Regulation | Continuous, precise | Automatic voltage regulator (AVR) | Minimal |
| Best For | Data centers, hospitals, mission-critical use | Small businesses, home offices | Personal computers, small electronics |
| Battery Usage | Always connected to load | Engages during outages | Engages only during outages |
| Cost | High | Medium | Low |
| Maintenance Requirement | High (complex systems) | Moderate | Low |
| System Size | Medium to large | Small to medium | Small |
| Noise and Heat Output | Higher | Moderate | Low |
Online Double Conversion UPS Systems
Online double conversion UPS is the most advanced and offers the highest protection level. They provide continuous power by converting the incoming AC power into DC power and back into AC power. This type of UPS is ideal for mission-critical applications requiring the highest protection level, such as data centers, hospitals, and other applications that cannot afford downtime. Online double conversion UPS uses a battery backup that is always connected to the equipment, providing uninterrupted power even during power fluctuations. In addition, the transfer time is typically zero, meaning it switches to battery power instantly when the input power fails.
Line-Interactive UPS Systems
Line-interactive UPS is suitable for small businesses and home offices. They provide basic power protection and battery backup and are easy to install and maintain. Line-interactive UPS uses an automatic voltage regulator to stabilize the voltage of the AC power supply, ensuring that equipment remains safe from damage. In addition, they have a short transfer time, typically between two to four milliseconds, which means they switch to battery power quickly when it fails.
Standby UPS Systems
Standby UPS is the most basic type of UPS suitable for personal computers and small electronic devices. They provide power protection and battery backup, but the transfer time can be up to 10 milliseconds, which means there may be a brief interruption in power when the unit switches to battery power.
How does a UPS work?
A UPS works by providing a backup power source to protected equipment during a power outage or any other interruption that may cause data loss or equipment damage. When the input power fails, the UPS switches to battery power instantly, providing uninterrupted power to sensitive equipment. In addition, the battery backup takes over the power supply during a power outage, ensuring no loss to sensitive equipment and continuing operations seamlessly until AC electricity is restored. Explore the benefits of High Efficiency UPS Systems that reduce energy waste while maintaining reliability.
Sensitive electronic equipment requires a clean and stable power source to function correctly. Power conditioning ensures that the voltage and frequency of the supply are stable, providing the necessary power source to keep equipment running without interruption. In addition, UPS provides surge protection, protecting equipment from surges and spikes, which can cause significant business losses. It can also protect equipment from lightning strikes that can cause significant damage.
The battery backup typically uses Valve Regulated Lead Acid (VRLA) batteries, which are maintenance-free and have a long lifespan. The lifespan depends on several factors, including the unit's quality and its maintenance. Emergency standby power supplies with regular maintenance can last anywhere from three to ten years. To maintain your unit, you should keep it in a clean, cool, and dry environment and perform regular maintenance, such as cleaning the battery terminals and checking the battery's charge level. It is also essential to replace the battery backup periodically, typically every two to three years, to ensure that your unit continues providing reliable backup power.
Common Power Problems
Power failures, power outages, and other common problems can cause significant business losses due to data loss and equipment damage. It is crucial for protecting sensitive equipment during these interruptions, ensuring smooth operations and reducing downtime. It offers protection, backup supply, conditioning, surge protection, management, and emergency power supply, reducing the risk of data loss and equipment damage. In addition, they are eco-friendly, help to reduce a company's carbon footprint, and extend the lifespan of sensitive electronic equipment, reducing the need for replacement. If you're wondering about battery lifespan, read our guide on How Long Do Battery Backups Last and what factors affect their performance.
How do I select the right kind?
When selecting a unit, businesses must consider their specific needs and budget. They come in various sizes, from small units that can provide backup power to a single computer to large units that can feed entire data centers. Businesses must also consider the runtime, which is the duration for which the system can provide backup power. The runtime depends on several factors, including the battery's size and the equipment's energy consumption. For help choosing the right solution for your facility, see our expert Tips for Selecting a UPS System.
Related Articles
UPS Risks - Surge Protection For Critical Loads
UPS risks include battery failure, overload, harmonics, thermal stress, poor grounding, EMI/RFI, and inadequate maintenance, leading to downtime, reduced power quality, inefficiency, and safety hazards in critical electrical systems operations.
What Are UPS Risks?
UPS risks are failure modes like battery faults, overload, harmonics, and EMI that degrade reliability and safety.
✅ Thermal runaway and VRLA battery degradation reduce runtime.
✅ Overload and inrush cause breaker trips, bypass transfer.
✅ Poor grounding and harmonics increase EMI, heating, failures.
The use of computers and other electronic systems has skyrocketed, and with it, so has the need to protect these systems from damage and service interruptions. Uninterruptible and stand-by power systems were created to fill the gap when sudden power disturbances threaten the operation of electronic equipment. However, there is a general is conception that UPS systems offer adequate protection against all major power disturbance problems including outages, noise, line regulation and voltage transients. For a clear overview of components and functions, this guide to what a UPS system is explains the basics in plain terms.
Unfortunately, UPS systems often do not adequately protect against voltage transients. Using a UPS system as the sole source of protection from power problems will leave computers and other electronics vulnerable to several distinct risks. Three key equipment risks to consider when evaluating UPS or stand-by power systems are harmonic distortion, the volume of bypass mode switching, and transient surges. To understand where protections begin and end, an uninterruptible power supply primer outlines typical capabilities and limitations.
HOW UPS AND STAND-BY SYSTEMS WORK
In a UPS system, alternate current (AC) utility voltage is converted to direct current (DC) voltage through the rectifier circuit in the converter section to charge the battery and supply the inverter. The inverter changes the DC voltage back to 60—cycle AC power to feed the attached equipment. When the utility AC voltage has failed or falls outside a preset electrical tolerance, the battery alone supplies DC voltage to the inverter section until the utility AC voltage is restored or the battery runs down. For a deeper dive into conversion stages and battery roles, an UPS power supply overview details common topologies and functions.
A stand-by power supply consists of the same basic components as a UPS with a rectifier circuit maintaining a charge on a battery. The key difference is that a stand-by system operates primarily in the bypass mode, meaning the raw utility AC voltage passes directly through the system to the equipment load unless the utility voltage fails or runs outside set limits. When this happens, a transfer switch shifts the load to an inverter, changing battery power to AC until utility power is restored or the battery drains. Because the utility AC power must be outside preset limits before the equipment load is switched to the inverted battery power, this transfer can result in as much as a full cycle of voltage dropout. For context on alternative architectures and transfer characteristics, this UPS system overview contrasts stand-by, line-interactive, and double-conversion designs.
HARMONIC DISTORTION RISKS
Depending upon the type of power supply used, harmonic distortion can heavily impact computer system operations. In the past, linear power supplies were often used, but switch mode power supplies that are much more susceptible to operational upset from harmonic distortion have all but replaced these linear systems. We tested a number of UPS systems for harmonic distortion and found that, even under no-load conditions, their harmonic distortion exceeded the standard three per cent limit. When we subjected these UPS systems to tests including linear and complex loads, their harmonic distortion increased dramatically. Some modern solutions address THD with improved PFC stages and filtering, and this high-efficiency UPS guide discusses design approaches and trade-offs.
BYPASS SWITCHING RISKS
Our tests on UPS systems also uncovered a higher than expected volume of switches to the bypass line, including instances when the test load was less than the unit’s load rating. This bypass switching can allow raw utility power and transient voltages directly through to the equipment load more often than expected. Of course, stand-by systems operate this way by design, but in both cases, raw power holds the potential to damage the equipment load. Properly sizing equipment per UPS ratings can reduce nuisance bypass events and better protect sensitive loads.
TRANSIENT SURGE RISKS
A power line disturbance engineering study revealed that a mere 0.5 per cent of the power disturbances during the test period was due to outages, only an additional 11 per cent was attributed to over and under voltages. The majority, 88.5 per cent of occurring disturbances, was caused by transient voltage (DV/DT) conditions. When selecting protection, practical UPS selection tips emphasize surge suppression specifications, response times, and coordination with TVSS devices.
From: Power Quality, Grounding & UPS Handbook, Vol 12, The Electricity Forum
Related Articles
Emergency Backup Generator
Emergency backup generator ensures standby power during outages, with automatic transfer switches, diesel or natural gas fuel, load management, and kW sizing to protect critical systems, homes, and businesses with reliable resilience.
What Is an Emergency Backup Generator?
An emergency backup generator is a standby power system that automatically restores electricity to critical loads.
✅ Automatic transfer switch engages within seconds
✅ Supports diesel, natural gas, or propane fuel
✅ Sized by kW, load priority, and runtime requirements
An emergency backup generator is a device that generates electrical power during an unexpected power outage or interruption in the power supply. Various factors, including natural disasters, severe weather conditions, or equipment malfunctions, can cause power outages. A unit can be a lifesaver in such situations, providing temporary power to essential appliances and keeping the lights on until power is restored. For an overview of emergency power supply concepts, see this introduction to emergency power supply for additional context.
Emergency backup generators come in different sizes and types and are typically powered by gasoline, diesel, natural gas, or liquid propane. Portable generators are typically smaller and can be moved around, while home standby generators are larger and permanently installed outside the home. Portable generators are an excellent choice for powering small appliances, while standby generators are more powerful and can supply power to an entire home.
When choosing a unit, it's important to consider the fuel source and the generator's power output. Generators run on different fuel types, and each type has advantages and disadvantages. Gasoline generators are commonly used due to their affordability and easy availability, but they require frequent refuelling and can be noisy. Diesel generators are more fuel-efficient and can provide longer run times but are typically more expensive. Natural gas and liquid propane generators are clean-burning and can provide uninterrupted power for extended periods, but they may require professional installation and can be expensive.
Generators work by converting mechanical energy into electrical energy. The fuel source powers the generator's engine, and the engine's motion is then converted into electricity by a generator alternator. The unit's power output is measured in watts, and the generator's wattage should be sufficient to power the essential appliances and devices during a power outage. However, it's important to note that a generator can power not all appliances and devices, and some may require a larger generator or an electrical panel upgrade.
An emergency generator should always be installed and operated according to the manufacturer's instructions to ensure safety and reliable performance. Portable generators should never be operated indoors, as they emit carbon monoxide and can cause deadly carbon monoxide poisoning. Extension cords should also be used to connect appliances to the unit, as improper use of extension cords can result in electrical shock or fire.
There are two types of home standby generator systems: manual transfer switches and automatic transfer switches. A manual transfer switch requires the homeowner to manually switch the electrical load from the utility power source to the unit. On the other hand, an automatic transfer switch automatically switches the load to the generator when the utility power goes out. An automatic transfer switch is a more convenient and reliable option. It ensures that the generator will start automatically and the essential appliances will be powered without manual intervention. For detailed specifications and selection guidance, review this automatic transfer switch resource to understand compatibility and code requirements.
Emergency backup generators are widely used in industrial, commercial, and institutional applications to provide reliable power during unexpected power outages. Here are some examples of how they are used in these settings:
Industrial Applications:
- Manufacturing plants: They are used to power critical manufacturing equipment during power outages, ensuring that production can continue without interruption.
- Oil and gas facilities: They power essential equipment such as pumps, compressors, and instrumentation during power outages, preventing downtime and maintaining safety.
- Data centers power critical IT infrastructure such as servers and networking equipment, ensuring that data and systems remain operational during power outages.
In many industrial environments, pairing generators with an uninterruptible power supply helps bridge transfer gaps and protect sensitive controls.
Commercial Applications:
- Retail stores: They power essential equipment such as cash registers, refrigerators, and lighting during power outages, ensuring that the store can remain open and customers can shop safely.
- Office buildings: They are used to power critical systems such as elevators, security systems, and lighting during power outages, ensuring that employees can continue to work safely.
- Hotels and resorts: They power essential equipment such as elevators, lighting, and HVAC systems during power outages, ensuring guests remain comfortable and safe.
For retail and office continuity, an UPS power supply can maintain point-of-sale terminals and network gear until generators assume the load.
Institutional Applications:
- Hospitals and healthcare facilities: They power critical medical equipment such as ventilators, monitors, and life support systems during power outages, ensuring patient care is not interrupted.
- Schools and universities: They power essential equipment such as lighting, HVAC systems, and emergency communications during power outages, ensuring that students and staff remain safe and comfortable.
- Government buildings: They power critical systems such as emergency lighting, communications, and HVAC systems during power outages, ensuring that government operations continue uninterrupted.
Institutions that depend on life safety and communications often deploy a UPS system to ensure clean power during transfer events.
They are essential for ensuring critical operations can continue during unexpected power outages in various industrial, commercial, and institutional settings.
How does a generator work?
During an unexpected power outage, a generator produces electrical power from a fuel source. When the power goes out, the unit's engine is powered by gasoline, diesel, natural gas, or liquid propane. The engine's motion is then converted into electricity by a generator alternator via an electric start, which produces electrical power. This power is transferred through a transfer switch to the home's electrical system, powering essential appliances and devices until power is restored. For a step-by-step explanation of this process, consult this guide on how a generator works before planning your installation.
How does a generator work with other technologies?
A generator can be used with other technologies to restore power after a power outage. For example, a solar panel system can generate electricity during the day. A unit can provide power at night or when the solar panels are not generating enough power. A battery backup system can also store excess solar or generator power, providing power during an outage. To size and configure storage correctly, compare options in this battery backup overview for best results.
What are the benefits of having an emergency backup generator?
There are several benefits. The most significant advantage is that it provides reliable power during a power outage, ensuring that essential appliances and devices continue functioning. This can be particularly important for households that rely on medical equipment or have special needs. Knowing that your home and family are protected during an unexpected power outage can also provide peace of mind. Finally, it can add value to your home, as it is a valuable and desirable feature for potential buyers.
What size generator do I need for emergency backup power?
The size of the generator needed for emergency backup power depends on the power requirements of the appliances and devices that need to be powered during a power outage. Therefore, it's important to calculate the wattage requirements of the essential appliances and devices during a power outage and choose a unit with a power output that is sufficient to power them. A licensed electrician or generator installer can help you determine the appropriate generator size based on your specific power requirements.
How long will it run?
The run time depends on several factors, including the fuel source, generator size, and load demand. Depending on the fuel source and generator size, portable power generators can run on a single fuel tank for several hours to several days. Therefore, choosing a unit with sufficient fuel capacity and monitoring its fuel level during a power outage is important. Then, if additional run time is needed, other dual fuel can be added to the unit.
Can I use one indoors?
Portable generators should never be used indoors, as they emit carbon monoxide and can cause deadly carbon monoxide poisoning. On the other hand, home standby generators are designed for outdoor installation and can be safely used during a power outage.
What maintenance is required?
Regular maintenance is important to ensure the reliable operation of a unit. This includes regular oil changes, air filter replacements, and spark plug replacements. It's also important to periodically test a unit to ensure it functions correctly and address any issues before a power outage occurs. A licensed electrician or generator installer can guide your unit's specific maintenance requirements.
Related Articles
What Size Emergency Generator Do I Need?
You need an emergency generator sized to your total wattage needs. Smaller units, ranging from 5 to 7 kW, cover essentials such as lights, refrigerators, and sump pumps, while units with 20–22 kW provide reliable whole-home backup, including HVAC systems.
What Size Emergency Generator Do I Need?
Refers to the process of calculating backup power capacity to match the energy demands of a household or business during outages.
✅ Determines generator size based on watts, circuits, and load
✅ Ensures appliances, HVAC, and lighting operate safely
✅ Prevents underpowered or oversized generator selection
Emergency Generator Standby Power Training
Power Quality Analysis Training
Request a Free Emergency Generator Training Quotation
The first step in choosing a generator is calculating your total wattage requirements. Appliances and devices draw two types of power: running wattage, which keeps the equipment operating, and starting wattage, sometimes referred to as surge watts, which is required during startup. Motors, pumps, and compressors often demand two to three times their running watts to start. Identifying the highest starting load is critical to prevent overloading your generator. When considering emergency backup generator options, it is important to compare capacity, fuel type, and wattage requirements to ensure your unit can handle both essential and whole-home loads.
Running watts cover steady-state demand, while starting watts account for those momentary peaks. For example, a refrigerator might require 700 running watts but 2,200 starting watts. If you plan to run multiple appliances simultaneously, your generator must be sized to meet the total running watts plus the highest single starting wattage. Understanding the emergency power supply options available helps homeowners decide whether a portable, inverter, or standby generator best matches their outage risks.
Essential vs Whole-Home Backup
Many homeowners must choose between powering only essential appliances and covering the entire house. Essential circuits usually include lighting, refrigerators, sump pumps, medical devices, and communication equipment. A portable generator rated between 5,000 and 7,500 watts usually provides adequate backup power for these needs. For homes and facilities with sensitive electronics, pairing a generator with a battery backup system can extend runtime and protect against short interruptions.
For those seeking seamless operation during power outages, a home standby generator is often the most suitable solution. Whole-home units are permanently installed, connected through an automatic transfer switch, and can power air conditioners, electric stoves, and central heating systems. House generators in the 18- to 22-kW range are commonly used for whole-home backup, ensuring that air conditioning units and HVAC systems remain operational. Learning how does a generator work provides useful insight into why surge watts and starting loads play such an important role in choosing the right size.

Types of Emergency Generators
Different types of generators are available for both residential and commercial applications. Portable generators are mobile and fueled by gasoline or propane, offering versatility during short-term outages. Inverter generators deliver cleaner power for sensitive electronics, operate quietly, and can be paralleled for more capacity. Home standby generators are fixed installations that run on natural gas or propane, providing automatic protection without manual intervention.
When choosing a generator, consider whether you need portability, quiet operation, or a permanent, automated solution. Powerful generators may be ideal for critical facilities, while inverter generators are suitable for households prioritizing fuel efficiency and reduced noise. Exploring the electrical generators and UPS channel gives a broader view of technologies, ratings, and selection tips that can guide your generator sizing decision.
Fuel Considerations
Fuel type influences convenience, runtime, and maintenance. Portable units typically run on gasoline, though dual-fuel models also accept propane. Home standby generators commonly use natural gas supplied by a utility line or propane stored on-site. Natural gas provides an uninterrupted fuel supply and eliminates storage issues, but requires a sufficient supply line. Propane offers longer storage life and flexibility.
Air Conditioning and High-Demand Loads
Air conditioning units are often the deciding factor when choosing the right size generator. Central systems have compressors that require very high starting wattage. A 3-ton air conditioner can easily exceed 6,000 surge watts at startup. If cooling is optional, smaller window units may lower demand and allow downsizing. Carefully assessing the highest starting load ensures the generator can handle surge watts without stalling.
Choosing the Right Size Generator
To size a unit accurately, follow this process:
-
List all appliances you want powered during outages.
-
Record their running wattage.
-
Identify the appliance with the highest starting wattage.
-
Add total running watts plus the single highest starting wattage.
-
Select a generator that exceeds this figure, leaving a 20 percent safety margin.
This approach avoids undersizing, which risks tripping breakers, and oversizing, which increases cost and reduces efficiency. For critical applications such as data centers, designing data center UPS infrastructure demonstrates how generators and UPS systems work together to deliver reliable power continuity.
Emergency Generator Sizing Checklist
| Step | Action | Explanation |
|---|---|---|
| 1 | Identify all appliances and systems you want powered during an outage. | Start with essentials such as lights, refrigerator, sump pump, Wi-Fi, and medical devices. |
| 2 | Write down the running wattage for each device. | Check the appliance label or manual for the continuous power required. |
| 3 | Find the starting wattage of appliances with motors or compressors. | Items like an air conditioning unit, refrigerator, or pump need extra surge watts to start. |
| 4 | Add total running watts to the highest single starting wattage. | This combined total represents your minimum generator requirement. |
| 5 | Compare this number to generator ratings in running watts and surge watts. | Ensure the unit’s running capacity and surge rating both meet or exceed your needs. |
| 6 | Decide between essential-only coverage or whole-home backup power. | Smaller portable units cover essentials; home standby generators cover entire houses. |
| 7 | Consider fuel type: gasoline, propane, or natural gas. | Each has pros and cons for cost, storage, runtime, and convenience. |
| 8 | Choose from types of generators: portable, inverter, or standby. | Portable for flexibility, inverter for quiet, clean power, and standby for automatic operation. |
| 9 | Allow a safety margin of 20 percent above your calculated wattage needs. | Prevents overloads and ensures smoother operation during peak demand. |
| 10 | Plan for the installation, safe placement, and maintenance of the transfer switch. | A transfer switch prevents backfeeding; maintenance ensures long-term reliability. |
Practical Scenarios
An essential-only setup might include lights, a refrigerator, a sump pump, and a small air conditioning unit. Combined running wattage may reach 3,500 watts, with starting surges pushing requirements to 6,000 watts. In this case, portable generators or paired inverter generators can suffice.
A whole-home backup scenario, including a central air conditioner, electric water heater, and cooking appliances, could demand 18–22 kW. Here, a home standby generator fueled by natural gas is the most suitable option.
Maintenance and Reliability
Even the most powerful generators require maintenance. Portable models need regular oil changes, fuel stabilization, and safe storage. Home standby systems should be exercised monthly and serviced annually. Ensuring transfer switches are tested and circuits are balanced guarantees reliable performance when power outages strike.
The question of what size emergency generator I need is answered by calculating wattage requirements, balancing running watts with surge watts, and factoring in the highest starting load. Smaller portable units provide backup power for essential appliances, while whole-home standby systems fueled by natural gas or propane ensure uninterrupted comfort, including the operation of air conditioners and HVAC systems. By carefully selecting a generator, considering the fuel type, and planning for regular maintenance, you can achieve reliable protection against outages while avoiding the pitfalls of underpowered or oversized equipment.
Frequently Asked Questions
How do I size a generator for an air conditioner?
To size a generator for just your air conditioning unit, check the unit’s starting watts and running watts on the nameplate. Add at least 20 percent for surge protection. A central air conditioner usually requires a larger home standby generator, while a window unit may be supported by a portable or inverter generator.
What are surge, peak, and starting watts?
Surge watts, peak watts, and starting watts all describe the brief power spike needed when a motor-driven appliance starts. They are higher than running watts and critical for choosing the right size generator. If ignored, the generator can stall or overload.
Can a portable generator power my whole home?
A portable generator can power an entire home only if it has sufficient capacity and is connected to the home's electrical system through a transfer switch. Without this, backfeeding into utility lines is dangerous. For whole-home backup, most homeowners rely on a permanently installed standby generator.
Is natural gas better than propane for standby units?
Natural gas is convenient because it provides an unlimited supply and eliminates the need for storage, but it relies on an active utility line. Propane is stored on-site, lasts longer in storage, and offers flexibility during utility disruptions. The best choice depends on availability and risk of outages.
Related Articles
High-Efficiency UPS Systems
High Efficiency UPS Systems deliver double-conversion protection, low THD, high power factor, intelligent battery management for data centers, ensuring clean power, reduced losses, redundancy, advanced SNMP monitoring, and remote alerts.
What Are High Efficiency UPS Systems?
High Efficiency UPS Systems are UPS units that optimize conversion efficiency, power quality, and battery runtime.
✅ Double-conversion topology; low THD, >=0.9 power factor
✅ Modular N+1 redundancy; hot-swappable lithium-ion batteries
✅ SNMP/Modbus monitoring; advanced battery management
Energy efficiency for uninterruptible power supply (UPS) equipment is so important because they can influence UPS energy efficiency and can directly impact energy costs. This paper will compare the differences in energy efficiencies among various UPS topologies available today through laboratory testing. These studies demonstrate flywheel—based UPS technology achieves much higher efficiency ratings as compared to legacy battery based UPS systems, resulting in substantial cost savings over the life of the system. For context, understanding the basics of a UPS is essential, and resources like what is a UPS system explain core functions in more detail.
UPS systems provide power conditioning and backup power to mission critical facilities such as data centers, broadcast sites and hospitals. UPS systems protect these sites from voltage fluctuations such as surges and sags or frequency fluctuations and also provide ride-through or temporary power to bridge the gap between a power outage and the restoration of utility power or the transfer to a backup generator. The UPS uses a form of short-term (seconds to minutes) energy storage to assist in power conditioning and power bridging in the event of a complete outage. The most common and practical direct-current (DC) energy storage forms are chemical batteries (for example, lead acid, NiCd, and NiMH), flywheels and ultra-capacitors. To perform its two functions, a UPS requires energy—in this case electricity. For an overview of architectures and operating modes, see UPS uninterruptible power supply overview for context on how these elements interact.
The industry measures UPS efficiency as power out divided by power in with the UPS consuming a portion of the input power. The amount of energy consumed by the UPS represents energy lost or inefficiency. UPS inefficiency can waste 10 per cent or more of utility input within the UPS itself and is a significant concern for data center operators, utilities and policy makers. UPS inefficiency amounts to thousands of kilowatt hours per year wasted in the process of protecting even a medium-sized mission critical load. A deeper understanding of conversion stages and losses can be found in UPS power supply fundamentals that map components to typical efficiency impacts.
UPS EFFICIENCY DEFINED
The efficiency of a UPS, as defined by the International Electrotechnical Committee, is “the ratio of (active) output power to (active) input power under defined operating conditions,” where defined operating conditions refer to a specific per cent load and load type (linear/resistive versus non-linear). Active power is measured in watts or kilowatts. Manufacturers often publish UPS ratings and efficiency curves that help compare performance across load levels.
IMPORTANCE OF UPS EFFICIENCY
The power demands of data centers are significant and growing. The U.S. Environmental Protection Agency (EPA) estimated data centers consumed 61 billion kilowatt-hours (kWh) in 2006 at a total electricity cost of approximately $4.5 billion. The EPA’s baseline forecast predicts a near doubling of energy consumption by 2011 to more than 100 billion kWh and $7.4 billion, assuming current growth and efficiency trends (2). In its alternative forecast views, EPA identified adoption of higher efficiency UPS systems as a key factor in reducing data center power consumption (3). A study by Intel Corp. showed typical UPS systems as contributing six to seven per cent losses to overall data center energy use. Strategic placement, redundancy choices, and distribution design are covered in designing data center UPS infrastructure to align efficiency goals with reliability.
At the individual data center level, improving UPS system efficiency offers direct, 24-hour-a-day energy savings, both within the UPS itself and indirectly through lower heat loads and even reduced building transformer losses. When a full data center equipment load is served through a UPS system, even a small improvement in system efficiency can yield large annual cost savings. Pacific Gas & Electric (PG&E) estimates a 15,000 square-foot data center with IT equipment operating at 50 watt-per-square-foot requires 6.9 MWh (megawatt hour) of energy annually for the information-technology (IT) equipment. If the UPS system supplying that power has its efficiency improved by just five percentage points, the annual energy bill will be reduced by 384,000 kWh, or about $38,000 at $0.10 per kilowatt hour (kWh), plus significant additional savings from the reduced cooling load. Procurement teams can apply tips for selecting a UPS system to balance efficiency ratings with lifecycle service considerations.
COOLING REQUIREMENTS AS A FUNCTION OF EFFICIENCY
When evaluating a UPS and its efficiency, it is important to keep in mind the first law of thermodynamics that “energy can neither be created nor destroyed.” With respect to UPS systems, the difference in active input and output power represents heat loss as a result of the activity the UPS performs. Heat interferes with the environmental conditions in a defined space such as an electrical room and will ultimately drive the temperature up and potentially cause short- or long-term damage to equipment as it exceeds designed temperature thresholds. A sound design of an electrical room includes an air-conditioning or precision cooling system to maintain a certain temperature band. The lower the efficiency of the UPS, the more heat that is generated and the more cooling that is required in the room, driving up capital costs and the ongoing operational expenses of the cooling system. As a general rule of thumb for an efficient centralized cooling plant, it takes 0.33 kW of power to cool one kilowatt of heat. As a result, the operational cost of a low efficiency UPS is further exacerbated by the additional cooling cost. Thermal performance features and maintenance guidelines in uninterruptible power supply best practices can further mitigate cooling overheads in dense rooms.
FACTORS IMPACTING UPS EFFICIENCY
There are two key factors influencing UPS system efficiency: the topology of the UPS system itself and the design of the data center’s power supply and distribution, which determines the load factor of the UPS.
UPS TOPOLOGY
The design of the UPS system itself has a significant impact on efficiency. Put simply, some UPS designs are inherently more efficient than others. There are two major topologies in use today in mission critical facilities—parallel online (also known as line interactive) and double conversion.
From: Power Quality, Grounding & UPS Handbook, Vol 12, The Electricity Forum