Understanding NEC 250.122: Equipment Grounding

nec 250.122

NEC 250.122 is a critical section of the National Electrical Code (NEC) that outlines the minimum size requirements for equipment grounding conductors. This standard is vital in ensuring electrical safety, as it determines the proper conductor size based on the rating of the overcurrent protection device. By following the guidelines, electricians and engineers can prevent electrical hazards such as overheating, equipment failure, and potential fire risks. Proper application of this standard is essential in both residential and commercial installations, safeguarding systems from grounding issues and ensuring compliance with safety regulations.


What Does it Cover in Terms of Equipment Grounding Conductor Sizing?

It specifies the minimum size of the equipment grounding electrode conductor required for a circuit. The size of the conductor is based on the rating of the overcurrent protection device (such as a circuit breaker) that is used to protect the circuit. Table 250.122 in the NEC provides detailed guidelines on the minimum size for these conductors. These sizes are determined based on the size of the overcurrent protective device and ensure the conductors can handle fault currents safely.

The primary goal of NEC 250.122 is to ensure that the equipment grounding conductors (EGC) are appropriately sized to carry any fault current back to the source, preventing electric shock and reducing the risk of electrical fires. It covers both the minimum size for new installations and the requirements for when the conductors need to be increased in size due to various factors.


How Do I Use NEC 250.122 to Calculate the Correct Size for a Grounding Conductor?

Calculating the correct equipment earthing conductor size begins with identifying the rating of the overcurrent protective device. For example, if you are using a circuit breaker rated for 100 amps, you will consult NEC Table 250.122, which specifies that for a 100-amp device, the minimum conductor size would be No. 8 copper or No. 6 aluminum. The size of the EGC must correspond with the overcurrent protection to ensure that it can safely carry fault currents without overheating.

However, in certain circumstances, the conductor size must be adjusted. For instance, if the conductors carrying current are upsized to accommodate voltage drop or for long runs, the EGC may also need to be increased in size according to the guidelines in NEC 250.122(B).


What Happens If the Equipment Grounding Conductor Is Undersized as per NEC 250.122?

Using an undersized equipment conductor can have serious safety implications. If a fault occurs, and the conductor cannot carry the fault current back to the source effectively, the risk of electric shock increases significantly. The conductor may overheat, leading to insulation failure, potential fire hazards, and damage to equipment. Therefore, it is crucial to ensure that the conductor meets the minimum size requirements set forth by the National Electric Code.

Undersized conductors also violate the requirements, which can result in non-compliance issues during inspections and potential fines or mandates to rewire portions of the system to meet code standards.

 

Does NEC 250.122 Apply to Both Residential and Commercial Installations?

Yes, it applies to both residential and commercial installations. Whether the system is for a single-family home, an office building, or a large industrial facility, the same principles of equipment earthing apply. The size of the conductor must be calculated based on the size of the overcurrent protection device in both residential and commercial settings.

However, larger commercial or industrial systems often require more complex earthing strategies, and factors such as system earthing and grounding electrode conductors must also be considered. In all cases, it is important to consult the NEC and, if necessary, seek the advice of a professional electrician or engineer to ensure that the system is compliant and safe.


How Do Adjustments for Voltage Drop Affect Equipment Grounding Conductor Sizing Under NEC 250.122?

Voltage drop occurs when the voltage decreases as electrical current travels through a conductor. This is more pronounced over long distances. According to the 2017 NEC, if the carrying conductors of a circuit need to be upsized to reduce voltage drop, the equipment grounding conductors (EGC) may also need to be upsized to match. This adjustment ensures that the conductor is adequate to handle fault currents, even when the current-carrying conductors are larger than standard.

The NEC requires that the conductor size be increased proportionally to the current-carrying conductor. For example, if you increase the size of the circuit conductors due to a long run, you should check NEC Table 250.122 to determine the correct proportion for upsizing the EGC to ensure compliance with the code.

It is is a crucial part of the National Electric Code, providing clear guidelines for the sizing of equipment conductors in various electrical systems. Earthing is essential for safety, preventing electrical shocks, fires, and damage to sensitive equipment. By ensuring that the conductors are properly sized based on the size of the overcurrent protective device, and adjusting for factors such as voltage drop, you can ensure compliance with the 2017 NEC and maintain a safe and effective electrical system.

Understanding and following the guidelines is critical for both residential and commercial installations, as it ensures the integrity and safety of the overall electrical system. Always consult the code, refer to NEC Table 250.122, and, if necessary, seek professional advice to ensure your installation is both safe and compliant.

Understanding NEC 250.122: Equipment Grounding On-Line Buyer's Guide

The Electricity Forum Online Industrial Electrical Power Buyer's Guide is an interactive reference tool for buyers and specifiers, providing information on equipment, companies, products and services for North America's electrical industry. Search through hundreds of leading Suppliers and thousands of product categories. Add Your Company Today!

Free Understanding NEC 250.122: Equipment Grounding Magazine Subscription

The Electricity Forum is a North American "value added" publisher of Transmission & Distribution print/digital magazine: Electricity Today - a leading electrical transmission and distribution magazine. Magazine is distributed FREE of charge to North American electrical industry professionals.

Contribute To The Electricity Forum

The Electricity Forum is interested in publishing your technical, non-commercial articles, on a wide variety of subjects. We are seeking original content for our Transmission and Distribution Channels. Click here to view our author guidelines and submit your article today!