Arc Flash Boundary Chart: How to Determine Safe Distances

An arc flash boundary chart is an essential tool for electrical workers and safety professionals to ensure that workers are adequately protected from the hazards of electrical incidents. The arc flash boundary, sometimes called the "protection boundary or minimum approach distance," is the minimum safe distance from energized electrical equipment, and it's critical to calculate this zone for each piece of equipment accurately.
Request a Free Training Quotation
The NFPA 70E and CSA Z462 standards provide guidance on how to use and calculate the arc flash boundary chart. It's essential to follow these standards and provide specialized training to qualified workers to ensure that they know the hazards and how to work safely around energized electrical equipment.
Implementing an effective electrical safety program that includes accurate calculations, appropriate PPE, and specialized training for workers is critical to protect workers from the hazards of electrical explosions.
What is an Arc Flash Boundary?
A hazard zone is a designated area around energized electrical equipment where an electrical explosion could cause serious injury or death to a worker not wearing the appropriate personal protective equipment (PPE). The protection zone is a critical component of electrical safety programs, as it helps to identify potential danger areas and ensure that workers are aware of the hazards.
These boundaries are established based on the incident energy that could be released during an electrical explosion. Incident energy is the thermal energy that could be released during an incident energy event, measured in calories per square centimetre (cal/cm²). The higher the incident energy, the greater the potential for injury and the larger the hazard zone.
To delve deeper into the specifics of boundaries, consult our article on Arc Flash Boundary.
What are AF Boundaries?
The protection zone is the minimum safe distance from the energized equipment that an unqualified worker can approach without wearing PPE. The NFPA 70E and CSA Z462 standards provide guidance on the minimum distances that should be maintained between energized electrical equipment and workers based on the incident energy levels.
There are three protection boundaries that are defined by the NFPA 70E and CSA Z462 standards:
Limited Approach Boundary (LAB) - The LAB is the minimum distance from the energized equipment that an unqualified person can approach. This zone is generally marked with a yellow line and is intended to keep unqualified personnel from entering the hazard zone.
Restricted Approach Boundary (RAB) - The RAB is the minimum distance from the energized equipment a qualified worker can approach without wearing the appropriate PPE. This zone is marked with a red line and indicates the point where a worker must begin wearing the appropriate PPE to prevent injury.
Prohibited Approach Boundary (PAB) - The PAB is the closest distance to the energized equipment considered safe for any person to approach, regardless of PPE. This zone is marked with a black line and is used to indicate the most hazardous area.
What is the Minimum Arc Flash Boundary?
The minimum arc flash boundary is determined by the incident energy level that could be released in the event of an electrical explosion. The incident energy level is calculated using complex mathematical formulas that consider the system voltage, available fault current, and the time the protective devices take to clear the fault.
The NFPA 70E and CSA Z462 standards provide tables and formulas to help calculate the incident energy and the minimum distance. The minimum approach distance is the distance from the energized equipment where the incident energy is below 1.2 cal/cm², which is the level of thermal energy that can cause second-degree burns to unprotected skin.
What is the Arc Flash Boundary for 480V?
The protection zone for 480V equipment can vary depending on the incident energy level. However, the NFPA 70E and CSA Z462 standards provide a table that specifies the minimum distance for 480V equipment based on the available fault current and the protective device clearing time.
For example, if the available fault current is 10,000A and the protective device clearing time is 0.1 seconds, the minimum approach distance for 480V equipment is 3 feet for a category 1 PPE level.
It's important to note that the minimum approach distance can vary depending on several factors, including system voltage, available fault current, and protective device settings. Therefore, it's essential to accurately calculate the proper working distance for each piece of equipment to ensure that workers are adequately protected.
How the Arc Flash Boundary Chart Is Used in the Field
The chart is a visual reference that helps safety managers, engineers, and qualified electrical workers quickly determine safe working distances based on incident energy levels. Typically, the chart displays boundary distances for various voltages, fault clearing times, and working distances. It’s used during risk assessments and job planning to decide how close personnel can be positioned to energized equipment without exceeding the 1.2 cal/cm² threshold. By consulting the chart, professionals can select appropriate PPE and ensure that labeling and signage reflect accurate hazard zones.
How to Calculate Boundaries
The chart can be used to calculate the minimum approach distance, but requires an understanding of the electrical system and its potential hazards. The process involves a detailed analysis of the electrical system and the potential fault currents that could occur.
The NFPA 70E and CSA Z462 standards provide guidance on calculating the protection zone using various methods, including the incident energy analysis method and the PPE category method.
The incident energy analysis method involves performing a detailed electrical system analysis to determine the potential incident energy levels at different points in the system. This method requires complex calculations and detailed information about the system components, such as the available fault current and protective device settings.
Based on the incident energy level, the PPE category method determines the minimum PPE level required for a specific task. This method involves using tables to identify the required PPE level for a specific incident energy level and selecting the appropriate PPE based on the task.
Regardless of the method used, ensuring that this safe distance is accurately calculated is critical to provide adequate worker safety.
Can an Unqualified Person Cross the AFB?
An unqualified person should never cross the LAB of an energized piece of electrical equipment. The LAB is the minimum distance from the energized equipment that an unqualified person can approach, and it's intended to keep unqualified personnel from entering the hazard zone.
Only qualified workers who have received specialized training and are authorized to work on or near energized electrical equipment should cross the RAB. Crossing the RAB without appropriate PPE is dangerous and can result in severe burns, injuries, or even death.