What Is A Current Transformer?
By Colin P. Hurst, Associate Publisher
By Colin P. Hurst, Associate Publisher
Our customized live online or in‑person group training can be delivered to your staff at your location.
A current transformer is an instrument transformer that steps down high primary current to a standard 5 A or 1 A secondary using a fixed ratio, enabling accurate current measurement, protection relays, and safe monitoring in electrical power systems.
A current transformer (CT) converts high system current to a proportional, lower secondary current using a defined turns ratio and is connected in series with the conductor. The secondary output, expressed in amperes, allows metering and protection devices to operate without direct exposure to high current levels.
It is the standard instrument transformer used specifically for current measurement and should not be confused with potential transformers, which are used for voltage measurement, or other sensing devices that do not provide proportional current scaling.
Current transformers are one of the two primary types of instrument transformers, alongside potential transformers, and serve as current-measuring devices in metering and protection systems.
By reproducing the primary current at a reduced level, the CT provides an accurate reference signal for monitoring and control. A current transformer measures current only; it does not measure voltage or transfer usable power, distinguishing it from voltage and power transformers, which serve different functions.
A current transformer operates on the principle of electromagnetic induction. The primary conductor, connected in series with the circuit, generates a magnetic field proportional to the current flow. This induces a corresponding current in the secondary winding.
The relationship between primary current and secondary current is defined by:
Ip / Is = Ns / Np
This ratio ensures that the secondary current accurately represents the primary current under rated conditions. Standard secondary values such as 5 A or 1 A allow consistent integration with metering and protection systems, which are part of the broader measurement framework described in Instrument Transformers.
Download our FREE Electrical Training Catalog and explore a full range of expert-led electrical training courses.
Current transformers are designed for accuracy under defined load conditions rather than energy transfer. Their performance is specified using accuracy class and burden, similar to how electrical characteristics are defined in Transformer Ratings.
Accuracy class indicates how closely the secondary current matches the scaled primary current. Metering classes such as 0.1, 0.2, and 0.5 are used for precision measurement, while protection classes such as 5P10 define behavior during fault conditions.
Burden, measured in volt-amperes (VA), represents the total load connected to the secondary circuit. Excessive burden increases the ratio error and phase angle error, reducing measurement accuracy.
In practice, even small changes in burden or wiring can introduce measurable error, directly affecting relay performance and metering accuracy.
A current transformer must never be operated with an open secondary circuit. If the secondary is open while current flows in the primary, dangerously high voltages can develop due to the collapse of magnetic flux.
Proper grounding and maintaining a closed secondary circuit are essential for safe operation. This isolation function complements the role of an Isolation Transformer, although a CT is designed for current measurement rather than voltage separation.
Current transformer designs vary based on application and installation requirements.
Wound-type CTs use a dedicated primary winding and are used in low-current systems.
Bar-type CTs use a conductor or busbar as the primary and are common in high-current applications.
Toroidal CTs allow conductors to pass through the core and are widely used in protection and leakage detection.
Split-core CTs can be installed without disconnecting conductors and are commonly used for retrofitting and temporary measurement.
These variations exist because installation method, system configuration, and accessibility requirements influence how the current measurement must be implemented safely.
Current transformers are used wherever electrical current must be measured, monitored, or used for protection logic in power systems.
Common applications include:
• Metering systems for energy and load monitoring
• Protective relays for fault detection and system protection
• Generator and feeder protection schemes
• Power system analysis and diagnostics
In these applications, the CT provides the current reference used by protection and measurement devices. This role works alongside voltage measurement devices such as the Potential Transformer, which provides the corresponding voltage signal in protection and metering systems.