Report calls for arc flash review on distribution secondary equipment

subscribe

In the 2012 National Electrical Safety Code, the approach for arc flash below 1000 volts V has changed. Now, utilities will have to review arc flash on distribution secondary equipment. The two main changes are at 480-V for metering and spot networks.

A recent report published by the Electric Power Research Institute EPRI titled, “480-V Distribution Arc Flash Updates” addressed these issues. The research conducted in 2011 concentrated on 480-V arc flash. For 480-V spot networks, research concentrated on information exchange and practices to manage arc flash in spot networks.

The main findings of this research were:

* IEEE 1584 is the predominate calculation method for spot networks with utilities assuming either an 18 or 24-inch 45.7 or 61.0-cm working distance.

* Many utilities are de-energizing the feeder for spot network work. This reduces fault current and energized buswork in protectors. Note that they are not operating a primary-side, oil switch.

* Work is manageable in many spot networks with heavy arc suits. 100 cal/cm2 suits are common.

* Utilities normally assume either a self-extraction time or assume that internal network protector fuses operate. Both assumptions allow work in many spot networks with available arc flash suits. Both assumptions also have disadvantages.

* External fuses or disconnects are a promising option to reduce incident energies and completely de-energize a network protector. These scenarios can be treated as open-air applications if the only exposure is line to ground.

For 480-V metering, several exploratory tests were performed on different meter styles to see if there were any units where the 20 cal/cm2 threshold would not apply. Tests showed that meters with significant internal busbar can have long durations and incident energies much higher than 20 cal/cm2.

Based on these new results, utilities should not work on 480-V meters with significant busbar that are energized without an analysis.

Related News

powerlines

ERCOT Issues RFP to Procure Capacity to Alleviate Winter Concerns

AUSTIN - The Electric Reliability Council of Texas (ERCOT) issued a request for proposals to stakeholders to procure up to 3,000 MW of generation or demand response capacity to meet load and reserve requirements during the winter 2023-24 peak load season (Dec. 1, 2023, through Feb. 29, 2024).

ERCOT cited “several factors, including significant peak load growth since last winter, recent and proposed retirements of dispatchable Generation Resources, and recent extreme winter weather events, including Winter Storm Elliott in December 2022, Winter Storm Uri in February 2021, and the 2018 and 2011 winter storms, each of which resulted in abnormally high…

READ MORE
Ontario Premier Doug Ford

Group of premiers band together to develop nuclear reactor technology

READ MORE

pickering nuclear plant

Ontario faces growing electricity supply gap, study finds

READ MORE

RBC agrees to buy electricity from new southern Alberta solar power farm project

READ MORE

power lines

Nearly $1 Trillion in Investments Estimated by 2030 as Power Sector Transitions to a More Decarbonized and Flexible System

READ MORE