Southern California Edison receives nuclear inspection report

subscribe

Southern California Edison SCE has received the Nuclear Regulatory Commission NRC Augmented Inspection Team report regarding the unusual degradation of steam generator tubes in the San Onofre Nuclear Generating Station SONGS Units 2 and 3.

The report provides comprehensive information on the issue, including the response actions by the SCE plant operators to the tube leak in Unit 3, the causes of the wear and the outstanding issues that the inspection team is still reviewing.

Tube-to-tube contact arises from excessive vibration of the tubes in certain areas of the steam generators. The excessive vibration is believed to be caused by a phenomenon called fluid elastic instability which results from the interaction of a combination of factors, including steam velocity, moisture content of the steam and effectiveness of the supports in the areas where the vibration occurs.

The report notes that SCE plant operators responded in a manner that protected public health and safety and that the commissionÂ’s onsite inspectors observed conservative decision-making and the appropriate questioning attitude displayed by the operators during the event.

"We are committed to continuing to work with the NRC on the steam generator issues and will continue to use conservative decision making as we work on repairs and planning for the future," said Senior Vice President and Chief Nuclear Officer Pete Dietrich. "The number one priority is the safety of the public and our employees."

Additionally, the commission report states that the steam generator design changes were appropriately reviewed in accordance with the 10 CFR 50.59 requirements, which govern design changes between original and replacement steam generators, noting that the changes at SONGS are common in replacement steam generators today.

The report also stated that, with the exception of the wear found at the tube retainer bar locations, the wear related to support structures is similar to wear found at other replacement steam generators after one cycle of operation.

SCE continues to work on its response to the commissionÂ’s Confirmatory Action Letter, the formal step in the process of restarting Units 2 and 3. The company will not restart the units until the utility and the commission are satisfied it is safe to do so.

Both SONGS units are currently safely shut down for inspections, analysis and testing. Unit 2 was taken out of service Jan. 9 for a planned outage. Unit 3 was safely taken offline Jan. 31 after station operators detected a leak in a steam generator tube.

Related News

British solar power worker

New rules give British households right to sell solar power back to energy firms

LONDON - Britain’s biggest energy companies will have to buy renewable energy from their own customers under new laws to be introduced this week.

Homeowners who install new rooftop solar panels from 1 January 2020 will be able to lower their bills by selling the energy they do not need to their supplier.

A record was set at noon on a Friday in May 2017, when solar energy supplied around a quarter of the UK’s electricity. However, solar panel owners are not always at home on sunny days to reap the benefit. The new rules will allow them to make…

READ MORE
new zealand wind farm

As New Zealand gets serious about climate change, can electricity replace fossil fuels in time?

READ MORE

beaver nuclear plant

Nuclear plants produce over half of Illinois electricity, almost faced retirement

READ MORE

duke energy logo

Duke Energy reaffirms capital investments in renewables and grid projects to deliver cleaner energy, economic growth

READ MORE

DP Energy Sells 325MW Solar Park to Medicine Hat

DP Energy Sells 325MW Solar Park to Medicine Hat

READ MORE