Transformer Oil Analysis Explained
Transformer oil analysis evaluates dielectric strength, moisture, acidity, interfacial tension, and dissolved gases in insulating oil. It ensures transformer reliability, detects faults, prevents failures, and supports predictive maintenance in power distribution.
What is Transformer Oil Analysis?
Transformer oil analysis is a diagnostic process that tests insulating oil for moisture, acidity, and gases to monitor the condition of transformers, improve reliability, and prevent failures.
✅ Identifies dielectric strength, moisture, acidity, and interfacial tension levels
✅ Detects dissolved gases that signal faults, overheating, or arcing
✅ Supports predictive maintenance and ensures compliance with IEEE and IEC standards
This form of testing is a cornerstone of preventative maintenance for electrical engineering and maintenance professionals. Ensuring the optimal condition of insulating fluids is essential for the reliable and efficient operation of high-voltage equipment. Degraded oil reduces efficiency, accelerates insulation aging, and increases the risk of failures. Regular analysis enables the early detection of potential issues, allowing for timely corrective actions that extend transformer life and ensure an uninterrupted power supply. For utility transformers, where downtime can disrupt entire networks, ongoing transformer oil analysis is as critical as proper transformer oil filling.
Electrical Transformer Maintenance Training
Substation Maintenance Training
Request a Free Training Quotation
Transformer oil testing plays a crucial role in ensuring the health of equipment. It ensures that insulating liquids continue to provide cooling and insulation while preventing dielectric failure. With modern grids demanding greater reliability, oil analysis combined with condition monitoring has become a strategic tool for utilities and industries. Recognized standards, such as IEEE C57.104, IEC 60599, and ASTM methods, guide testing procedures, the interpretation of results, and recommended corrective actions. In modern systems, condition monitoring works in tandem with oil testing to detect early signs of faults and extend the lifespan of transformers.
Dissolved Gas Analysis
Dissolved gas analysis (DGA) is the most widely used diagnostic test for assessing the condition of electrical equipment. By identifying gases such as hydrogen, methane, ethylene, and acetylene dissolved in the fluid, engineers can detect thermal faults, arcing, or overheating long before physical symptoms appear. For example, acetylene may indicate high-energy arcing, while elevated hydrogen levels often signal partial discharge. By comparing gas concentrations against IEEE and IEC thresholds, operators can implement corrective actions before problems escalate. Because distribution transformers play a critical role in voltage delivery, routine DGA ensures reliable service to residential, commercial, and industrial customers. The role of distribution transformers necessitates regular analysis to ensure stable voltage delivery to residential, commercial, and industrial users.
Moisture Content
Moisture is one of the leading causes of reduced dielectric strength. Even small amounts of water in insulating fluids increase the risk of flashover and accelerate the degradation of paper insulation. Regular testing identifies water contamination early, allowing timely fluid treatment or replacement. Moisture analysis not only protects winding insulation but also provides valuable insight into transformer loading, breathing, and sealing conditions. For professionals studying transformer design, moisture control illustrates the importance of oil’s dual role as coolant and insulator. For engineers studying the construction of a transformer, oil analysis provides practical insight into how insulating fluids preserve coil integrity and cooling efficiency.

Dielectric Breakdown Voltage Testing
The dielectric breakdown voltage (BDV) test measures the maximum voltage oil can withstand before electrical breakdown occurs. This simple yet powerful test determines whether oil continues to provide adequate insulation under stress. Results guide maintenance decisions such as filtration, degassing, or replacement. When combined with advanced diagnostics, such as hydrogen detection or DGA, BDV testing provides a comprehensive picture of equipment readiness for demanding operating conditions. Advanced diagnostics, such as dissolved gas analysis, can complement specialized equipment like a hydrogen detection system, safeguarding against internal faults.
Acid Number
Acid number testing (also known as neutralization number) monitors the buildup of acidic compounds formed as oil oxidizes over time. High acid levels corrode metals, degrade insulation, and contribute to the formation of sludge, which reduces cooling efficiency. Tracking the acid number enables predictive maintenance planning and helps operators avoid accelerated transformer aging. In combination with furan analysis, acid testing provides a strong indicator of overall fluid degradation and the health of solid insulation. Understanding how oil testing supports the operation of high-voltage transformers highlights its importance in maintaining safe insulation and efficient energy transfer.
Comparison Table
| Aspect / Focus | Transformer Oil Analysis | Condition Monitoring | Hydrogen Detection System |
|---|---|---|---|
| Purpose | Evaluates insulating oil quality: moisture, acidity, dissolved gases, dielectric strength | Tracks overall transformer performance, detecting faults early | Detects hydrogen gas buildup from overheating or arcing |
| Key Parameters | Moisture, acid number, dissolved gas levels, dielectric breakdown voltage | Temperature, vibration, oil quality, load fluctuations | Hydrogen ppm levels in oil or the surrounding environment |
| Reliability Impact | Prevents insulation failure, extends transformer lifespan | Reduces unplanned outages, predicts maintenance needs | Prevents catastrophic failures and downtime |
| Maintenance Role | Guides oil treatment, replacement, or corrective action | Provides system-wide health insights for proactive maintenance | Enables fast response to internal transformer faults |
Interfacial tension (IFT)
Interfacial tension (IFT) testing, although less frequently discussed, is equally critical in evaluating quality. IFT measures the ability of an insulating fluid to separate from water. As fluid ages and becomes contaminated with byproducts of degradation, its interfacial tension decreases, indicating a loss in purity and efficiency. Ensuring high IFT values is essential for maintaining the insulating liquid's protective qualities and overall system performance.
Advanced Testing
Beyond standard tests, advanced diagnostics offer deeper insight. Furan testing detects cellulose breakdown, a key indicator of insulation aging. Power factor testing measures dielectric losses and reveals any deterioration in oil or insulation. Flash point testing evaluates fire safety by determining an oil’s resistance to ignition. Together, these tests provide a comprehensive health assessment, helping utilities maintain reliability, meet compliance requirements, and reduce lifecycle costs.
Routine transformer testing not only identifies immediate problems but also builds a historical database that improves long-term decision-making. Utilities, industrial plants, and service providers rely on these results to optimize maintenance schedules, extend equipment life, and improve grid stability.
Dielectric Fluid
Dielectric fluid examination also focuses on physical properties, such as flash point, which indicates the fluid's flammability and safety under operational conditions. A higher flash point denotes better thermal stability, ensuring the insulating liquid remains effective even in demanding environments. These parameters collectively highlight the importance of transformer oil testing and its role in safeguarding electrical systems. Maintaining the insulating fluid is just as vital as selecting the right dielectric fluid, since purity and dielectric strength directly affect operational safety.
Routine analysis not only identifies existing problems but also prevents potential failures, enabling a longer lifespan for critical assets. Electrical utilities and industries rely on these insights to maintain an uninterrupted power supply and reduce operational costs. By focusing on key themes such as dissolved gas analysis, moisture content, and acid number, this kind of analysis remains indispensable in modern power system management.
Frequently Asked Questions
What tests are done on a transformer?
Transformer oil is tested for moisture, acid number, dielectric breakdown voltage, and gases. Advanced methods include interfacial tension, furan testing, and power factor testing. Together, these tests provide a complete profile of insulation and oil condition.
How do you do oil analysis?
Oil analysis begins with proper sampling, followed by laboratory tests that utilize IEEE, IEC, and ASTM standards. Common tests include DGA, BDV, moisture, and acidity. Results are compared to benchmarks to detect issues and guide corrective maintenance.
How much does transformer oil sampling cost?
Costs vary by scope and provider. Basic testing (DGA, moisture, BDV) ranges from $200 to $500 per sample. Comprehensive packages with furan or advanced diagnostics may exceed $1,000. Despite costs, regular testing prevents failures and reduces long-term expenses.
How can the health of transformer oil be checked?
The health of insulating fluids is checked through routine tests, including DGA, BDV, moisture, acid number, and IFT. Advanced diagnostics and visual inspections supplement these methods, ensuring safe operation and extending service life.
Related Articles
Sign Up for Electricity Forum’s Dielectric Fluids Newsletter
Stay informed with our FREE Dielectric Fluids Newsletter — get the latest news, breakthrough technologies, and expert insights, delivered straight to your inbox.
Transformer Insulating Oil
Transformer Insulating Oil provides dielectric insulation, arc suppression, and cooling for power transformers, improving efficiency, preventing electrical faults, reducing downtime, and ensuring reliable high-voltage system performance in energy distribution networks.
What is Transformer Insulating Oil?
Transformer insulating oil is a vital fluid that plays a crucial role in the reliable and efficient operation of electrical power systems.
✅ Provides electrical insulation and suppresses arcing between components
✅ Dissipates heat to prevent transformer overheating and failure
✅ Protects against moisture, oxidation, and other contaminants
It serves as the lifeblood of power transformers, providing essential insulation, cooling, and arc-quenching properties. A deep understanding of the fluid's characteristics, functions, and maintenance requirements is essential for electrical engineers, technicians, and maintenance professionals to ensure the optimal performance and longevity of these critical components. To learn more about the role of dielectric fluids in transformer insulation and cooling, visit our main page on Dielectric Fluids.
Electrical Transformer Maintenance Training
Substation Maintenance Training
Request a Free Training Quotation
The essential role of transformer insulating oil in electrical power distribution systems cannot be overstated. This insulating fluid plays a vital role in ensuring transformers' efficiency, safety, and longevity. It is a crucial insulating material that supports electrical stability while also providing thermal management and arc-quenching capabilities. Without it, transformers would face higher risks of failure, overheating, and electrical breakdowns. For insight into cutting-edge techniques for fault detection, see our detailed guide on Advancements in DGA Data Quality.
One of the most critical aspects of this kind of dielectric fluid is its ability to act as an excellent electrical insulating medium. By filling the space around the core and coils, it prevents electrical arcing and ensures a high dielectric strength. This high dielectric strength is essential for maintaining insulation integrity under high-voltage conditions. The breakdown voltage of the insulating fluid must be tested regularly to ensure it retains its insulating properties. Testing procedures, such as dielectric strength testing and dissolved gas analysis (DGA), are used to identify potential issues and help maintain service life. Discover how dissolved gas patterns reveal transformer health in our technical article on Advancements in Dissolved Gas Analysis.
The properties of a dielectric fluid vary depending on its type. Mineral oil remains one of the most widely used types of transformer dielectric fluid due to its affordability, availability, and decent insulating performance. However, it’s not the only option. Synthetic ester oils offer a more sustainable and fire-resistant alternative. These oils have a high fire point, making them safer for use in sensitive environments where fire hazards must be minimized. Silicone-based dielectric fluids, on the other hand, are known for their ability to remain stable at high temperatures, offering an advantage in environments with extreme heat.
Insulation and Cooling
Another critical role of transformer insulating oil is heat dissipation. The design of transformers enables efficient heat transfer, allowing the insulating fluid to absorb and dissipate heat generated by the core and coils. This heat management is crucial for extending the service life. An essential property that supports this function is the pour point of the fluid, which ensures it remains fluid even at low temperatures. Fluid with a low pour point maintain fluidity, ensuring effective heat dissipation in colder climates. Dive deeper into diagnostic gas trends with our exploration of CO/CO₂ Ratio Analysis as an indicator of cellulose insulation degradation.
Arc Quenching and Oxidation Resistance
Regular transformer testing and maintenance are essential to maintaining the effectiveness of dielectric fluids. Filtration and purification are critical to remove contaminants, moisture, and gases that accumulate over time. Oxidation stability is one of the most important factors influencing the service life of the fluid. When oxidation occurs, it can form acids and sludge, which degrade the dielectric fluid's insulating properties and reduce its effectiveness. Regular filtration processes ensure the insulating oil remains pure and retains its excellent electrical insulating capabilities.
Testing and Maintenance
Regular testing and maintenance are essential to maintaining optimal performance and reliability. Dielectric strength testing measures the dielectric fluid's ability to withstand electrical stress, while dissolved gas analysis (DGA) identifies potential faults within the unit by analyzing the gases dissolved. Fluid filtration and purification techniques remove contaminants and moisture, prolonging the dielectric fluid's service life.
Types of Transformer Oil
Various types are available, each with its own specific characteristics. Mineral oil, a traditional choice, is derived from petroleum and offers a balance of performance and cost-effectiveness. However, it is susceptible to fire and environmental concerns. To address these issues, synthetic ester oils have emerged as a superior alternative. These dielectric fluids exhibit excellent fire resistance, high dielectric strength, and superior oxidation stability. They are also environmentally friendly and biodegradable. Silicone oil, another synthetic option, offers exceptional thermal stability and arc-quenching properties, making it suitable for high-temperature applications.
Environmental Impact and Safety
Environmental sustainability has also become a key consideration in the selection and management of dielectric fluid. Traditional mineral oil has environmental drawbacks, such as limited biodegradability and disposal challenges. Biodegradable types, such as synthetic ester oils, are now being used as environmentally friendly alternatives. These dielectric fluids offer the dual benefits of reducing environmental impact and providing high fire resistance. Moreover, responsible recycling and disposal practices for used transformer fluids are mandated by regulatory compliance standards to protect the environment.
Safety is a paramount concern when dealing with dielectric fluid. As the dielectric fluid circulates inside, it’s crucial to understand the risks associated with fire hazards. The flash point of a dielectric fluid is a key indicator of its fire resistance. Dielectric fluids with a high fire point are preferred in applications where fire safety is a priority. Emergency response procedures must also be established in the event of spills or leaks, ensuring that spills are contained quickly to prevent environmental contamination. Additionally, health and safety measures are critical for workers handling dielectric fluid. Direct exposure can pose health risks, requiring protective equipment and following established handling protocols. For additional context on cooling mechanisms and thermal performance, read our article on Transformer Cooling and Dielectric Fluids.
Frequently Asked Questions
What is another name for transformer oil?
Another name is insulating or dielectric fluid. It is also sometimes referred to as dielectric fluid because of its role as a dielectric material that prevents electrical discharges inside. In specific contexts, names like mineral-insulating dielectric fluid or ester-based insulating dielectric fluid may be used to specify the type of oil used.
Can I use transformer oil on my skin?
No, it is not recommended to use dielectric dielectric fluid on your skin. This oil is not designed for human contact and may contain chemical additives, contaminants, or degradation products that can irritate the skin. Prolonged exposure to certain types of mineral oil can pose health risks. Any exposure should be washed off immediately with soap and water for health and safety reasons.
What is the real name of transformer oil?
The real name depends on its composition. Most dielectric fluids are referred to as mineral insulating oil or naphthenic mineral oil. Biodegradable alternatives may be called natural ester insulating dielectric fluid or synthetic ester insulating oil. For example, common mineral oil used is a type of naphthenic oil, while modern, environmentally friendly units may use ester-based oils.
Transformer dielectric fluid is a vital component in electrical power distribution, playing a central role in insulation, cooling, arc quenching, and overall safety. The choice of dielectric fluid—whether mineral, synthetic ester, or silicone—depends on application requirements, safety considerations, and environmental impact. Regular testing, maintenance, and proper disposal methods ensure its continued performance and compliance with regulatory standards. By maintaining oxidation stability and leveraging dielectric fluids with a high fire point, operators can ensure the longevity and safety in various industrial and commercial settings.
Oil in Transformers - An Insulating Medium
Oil in transformers plays a critical role as a cooling and insulating medium which directly impacts the efficiency, performance, and lifespan, which are essential components of the power grid. Understanding its properties, maintenance requirements, and failure indicators can help professionals prevent costly outages and enhance grid reliability. Let's explore the key functions of dielectric fluid, common issues such as contamination and aging, and best practices for testing and maintenance, equipping readers with the knowledge to optimize device performance and safety.
Electrical Transformer Maintenance Training
Substation Maintenance Training
Request a Free Training Quotation
The Dual Function of Transformer Oil
The primary function of transformer-based oils is to provide both insulation and cooling. As the device operates, heat is generated from the core and coils due to electrical losses. Device liquid, typically filled with mineral oil or similar insulating fluid, absorbs this heat and dissipates it efficiently, thus preventing overheating. Moreover, it serves as an insulating material, maintaining the dielectric strength required for safe operation. The high dielectric strength of the liquid prevents electrical arcing or short circuits between components within the device, ensuring that the unit functions reliably. This dual-purpose function of the oil contributes significantly to the device’s ability to operate for extended periods without failure, reducing the risks of overheating and electrical faults.
Electrical insulating materials play a crucial role in maintaining the efficiency and safety of transformers by managing heat from the core and coils. Among the most commonly used materials, paper insulation provides effective thermal and electrical resistance, ensuring stable performance under operational stresses. Solid insulation, such as epoxy or resin-based materials, complements paper insulation by adding structural integrity and resistance to mechanical and thermal degradation. Together, these insulating systems work to optimize heat dissipation and prevent electrical faults, safeguarding equipment longevity and reliability.
Types of Transformer Oils
However, not all device oils are created equal. There are two main types of fluids used in devices: uninhibited oil and inhibited oil. Uninhibited liquid lacks additives that can slow down its natural degradation, making it more prone to breakdown over time. On the other hand, the inhibited liquid is enhanced with oxidation inhibitors that increase its resistance to degradation. This makes the inhibited liquid ideal for modern devices, where long-term stability and performance are crucial. As devices continue to serve in industrial and power distribution systems, the type of fluid used in each unit plays a direct role in its efficiency, lifespan, and overall environmental impact.
The Importance of Regular Testing and Quality Assessment
When it comes to device liquid, regular testing is essential to ensure that it maintains its properties over time. One of the most critical tests conducted is the dielectric breakdown voltage test, which measures thermal conductivity and the liquid's ability to withstand electrical stress without breaking down. This test ensures that the liquid can continue to insulate effectively under high-voltage conditions. Another important analysis is the Dissolved Gas Analysis (DGA), which detects gases dissolved in the liquid. The presence of certain gases can indicate internal faults, such as overheating or arcing, which could lead to a device failure. By performing regular tests, maintenance teams can identify potential issues early and take corrective action before they escalate into significant problems.
Environmental Considerations and the Shift Toward Sustainable Oils
Environmental considerations also come into play when selecting liquid for the device. Traditional mineral oils, while effective, pose certain environmental risks, such as fire risk and potential toxicity in the event of spills. As a result, alternative, environmentally friendly options, such as natural esters, are gaining popularity. These bio-based liquids and dry type transformers are derived from renewable sources and offer better biodegradability, making them a more sustainable option compared to conventional mineral oils. Additionally, their higher flash point reduces the fire risk associated with device operation, further contributing to the safety of electrical installations. However, while natural esters present a promising alternative, their adoption is still growing, and they are not yet as widespread as mineral oils.
Maintenance and Purification of Transformer Oil
As with any fluid used in electrical equipment, device liquid requires periodic maintenance and purification. Over time, device liquid can deteriorate due to oxidation, external contamination, or electrical stress breakdown. To ensure that the liquid retains its properties, purification techniques such as filtration or vacuum treatment are employed. These methods remove contaminants and restore the liquid’s insulating properties, helping to extend the life of the device. By maintaining the quality of the insulating liquid, power companies can avoid costly repairs and ensure that their devices continue to function efficiently for years.
Frequently Asked Questions
Which oil is used in the transformer?
The liquid used in devices is typically a type of mineral oil, which is specifically refined and treated to meet the insulating and cooling requirements of devices. However, natural esters, which are derived from renewable plant sources, are increasingly used as an environmentally friendly alternative. These liquids are selected for their high dielectric strength (the ability to resist electrical breakdown) and their ability to dissipate heat efficiently from the device's internal components.
What is the oil inside a transformer?
Oil filled transformers are dielectric fluid, meaning it does not conduct electricity and serves primarily to insulate the electrical components from each other. This liquid helps prevent electrical arcing and short circuits. In addition to its insulating properties, the insulating oil also acts as a cooling agent, absorbing and dissipating heat generated by the electrical currents passing through the device's core and coils. The liquid helps maintain the device at a safe operating temperature, preventing overheating and damage to the internal components.
How to maintain transformer oil?
To maintain liquid, regular testing is essential to monitor its dielectric strength, moisture content, and dissolved gases, which can indicate internal issues. Filtration and vacuum treatment help purify the liquid by removing contaminants like sludge, moisture, and gases. Monitoring liquid levels is crucial to ensure proper insulation and cooling while addressing leaks or evaporation. Over time, liquid may need to be replaced or upgraded, especially if it has degraded or become contaminated. By following a routine maintenance schedule, including inspections and necessary treatments, device liquid can be kept in optimal condition, ensuring the device operates safely and efficiently.
What happens if there is no oil in a transformer?
If a device runs without liquid or if the liquid level becomes too low, several critical problems can occur. The device would lack the necessary insulation and cooling properties provided by the liquid. Without adequate insulation, electrical arcing could occur, leading to short circuits or even fires. Additionally, the device would overheat because there would be no liquid to absorb and dissipate the heat generated by the electrical currents. Overheating can damage the device’s internal components, reduce its efficiency, and ultimately lead to the complete failure of the device. Therefore, maintaining an adequate liquid level is essential for a device's safe and efficient operation.
Oil in devices plays a critical role in both insulation and cooling, ensuring the efficient operation and longevity of the device. It acts as an insulating fluid, preventing electrical faults by maintaining a high dielectric strength, and absorbs heat generated during operation, preventing overheating. Equipment liquid can be mineral liquid or natural esters, with the latter being an environmentally friendly alternative. Regular maintenance, including testing for dielectric strength, moisture, and dissolved gases, along with purification methods like filtration and vacuum treatment, is necessary to keep the liquid effective. Proper oil management helps extend device lifespan, reduce risks of failure, and ensure safe, reliable operation in electrical systems.
Dielectric Fluid
Dielectric fluid is an insulating liquid used in electrical equipment like transformers and capacitors to prevent arcing, dissipate heat, and ensure system reliability. It offers high dielectric strength, thermal stability, and moisture resistance for safe operation.
What is Dielectric Fluid?
Dielectric fluid is a critical component in the operation and safety of electrical equipment, especially transformers and high-voltage switchgear.
✅ Provides electrical insulation and prevents arcing in high-voltage systems.
✅ Offers excellent thermal conductivity to dissipate heat.
✅ Protects components from moisture and contamination.
For industrial electricians, understanding their role in insulation, cooling, and arc suppression is essential for ensuring system reliability and preventing electrical failures. Let's review the properties, types, and maintenance requirements of dielectric fluids, providing practical insights into how they support energy efficiency, equipment longevity, and fire safety. Readers will learn about testing procedures, contamination risks, and how proper fluid management can minimize downtime and enhance overall electrical system performance. An oil-filled transformer relies on dielectric fluid to provide both insulation and cooling, ensuring safe and efficient operation.
Electrical Transformer Maintenance Training
Substation Maintenance Training
Request a Free Training Quotation
Applications in Electrical Equipment
In the realm of electrical equipment, insulating fluids are indispensable. They serve as both insulating and cooling agents, safeguarding systems from electric discharges while effectively dissipating heat. High-voltage applications, such as transformers, capacitors, and cables, rely heavily on these fluids to maintain stability and reliability. By preventing electric breakdown in these critical components, dielectric fluid ensures the longevity and efficiency of power distribution networks, which are the backbone of modern energy systems. The quality of transformer oil is crucial because its dielectric properties directly affect breakdown voltage and reliability.
Role in Immersion Cooling
The role of dielectric fluid in immersion cooling has gained prominence with the rise of data-intensive industries. Immersion cooling involves submerging electronic components in a thermally stable dielectric liquid to enhance heat transfer and reduce energy consumption. This technique is particularly advantageous in data centers, where efficient cooling solutions are essential. By dissipating heat more effectively than traditional air-cooling methods, dielectric fluid enables high-performance computing systems to operate at optimal levels while minimizing their environmental impacts. Understanding the role of transformer core and its interaction with insulating fluids can optimize cooling and extend transformer lifespan.
Comparison with Mineral Oils
A frequent comparison in the industry is between dielectric fluid and traditional mineral oil. While both serve as insulators and coolants, advanced dielectric fluid surpasses mineral oils in terms of thermal stability, oxidation resistance, and eco-friendliness. In high-voltage applications, \fluids offer lower operating temperatures and improved system reliability, reducing failure rates and extending service life. These properties make them an ideal choice for industries seeking to strike a balance between performance and sustainability.
Comparison of Dielectric Fluids
| Fluid Type | Key Properties | Advantages | Limitations |
|---|---|---|---|
| Mineral Oil | Moderate dielectric strength, good cooling, low cost | Widely available, proven track record | Low fire point, poor biodegradability |
| Natural Ester | High dielectric strength, high fire point (>300°C) | Biodegradable, excellent moisture tolerance | Higher cost, potential oxidation if unmanaged |
| Synthetic Ester | High thermal stability, excellent oxidation resistance | Long service life, superior high-temperature performance | Expensive, less eco-friendly than natural esters |
| Nanofluids | Enhanced dielectric strength and heat transfer via nanoparticles | Improved cooling, reduced aging, and emerging technology | Still experimental, higher production cost |
Types of Dielectric Fluids – Mineral Oil, Natural Ester, Synthetic Ester, Emerging Nanofluids
Dielectric fluid is categorized into several types, each with distinct properties and applications. Mineral oil has been the traditional choice due to its low cost and reliable insulation; however, it has limitations, including low flash points and environmental concerns. Natural ester fluids, derived from vegetable oils, offer high biodegradability, excellent moisture absorption, and fire safety advantages with fire points exceeding 300°C. Synthetic esters provide superior oxidation stability and thermal performance, making them suitable for high-load and high-temperature applications. Emerging nanofluids, enhanced with nanoparticles such as graphene or titanium dioxide, are at the forefront of innovation, offering improved thermal conductivity, higher dielectric strength, and enhanced aging resistance compared to conventional fluids. Regular testing of transformer oil filling is essential to avoid contamination and maintain high dielectric strength.

Material Compatibility & Impregnation – Testing Standards, Handling Guidance, Temperature Considerations
The interaction of dielectric fluids with insulation materials, gaskets, and seals plays a vital role in system performance. Certain fluids can cause swelling, shrinkage, or chemical degradation of elastomer-based gaskets, leading to leaks or compromised insulation. Modern ester fluids often require gasket materials that are highly resistant to hydrolysis and oxidation, such as nitrile or fluorocarbon elastomers, which offer superior stability compared to standard rubber seals.
Solid dielectrics, like pressboard or paper insulation, are directly affected by fluid absorption and impregnation. A properly selected fluid not only insulates but also strengthens these materials by filling microscopic voids and preventing moisture ingress. Poor fluid-material compatibility can reduce dielectric strength and lead to premature equipment failure.
The impregnation process, often carried out using vacuum-pressure cycles, ensures that the fluid thoroughly saturates the cellulose insulation. Vacuum impregnation removes trapped air and moisture before fluid introduction, improving dielectric performance and reducing the risk of partial discharges. Heating the fluid slightly during impregnation enhances its flow properties and ensures deep penetration. Standards like ASTM D3455 are used to verify material compatibility, while strict handling guidelines prevent contamination and degradation during storage. Proper transformer insulation depends on the fluid’s ability to prevent arcing and maintain thermal stability under load.
Material Compatibility and Impregnation Guidelines
| Aspect | Key Details | Recommended Standards/Tests | Notes and Best Practices |
|---|---|---|---|
| Gasket Compatibility | Evaluates swelling, shrinkage, and chemical stability of elastomers | ASTM D3455 (Compatibility Testing) | Use nitrile or fluorocarbon gaskets for ester-based fluids |
| Solid Dielectrics | Interaction with pressboard, paper, or cellulose insulation | IEC 60296 (Insulating Liquids) | Ensure low-moisture fluids to prevent insulation breakdown |
| Impregnation Process | Saturation of solid insulation with dielectric fluid | Vacuum-Pressure Impregnation Methods | Perform multi-cycle vacuum drying for optimal saturation |
| Handling Guidance | Preventing contamination during storage and transfer | ASTM D923 (Sampling Insulating Liquids) | Use sealed containers and moisture-proof handling systems |
| Temperature Control | Managing viscosity and flow during impregnation | ASTM D3487 (Transformer Oils) | Preheat fluid slightly (40–60°C) for better impregnation |
Influence on Gaskets and Dielectric Materials
The compatibility of insulating fluids with gaskets, seals, and solid dielectric materials is critical for the long-term reliability of electrical equipment. Certain fluids can cause swelling, shrinkage, or chemical degradation of elastomer-based gaskets, leading to leaks or compromised insulation. Modern natural and synthetic ester fluids often require gasket materials that are highly resistant to hydrolysis and oxidation, such as nitrile or fluorocarbon elastomers, which offer superior stability compared to standard rubber seals.
Solid dielectrics, like pressboard or paper insulation, are directly affected by fluid absorption and impregnation. A properly selected fluid not only insulates but also strengthens these materials by filling microscopic voids and preventing moisture ingress. Poor fluid-material compatibility can reduce dielectric strength and lead to premature equipment failure.
Performance Metrics & Diagnostics – Presenting Typical Values, Standards, and Testing Procedures
Key performance metrics for insulating fluids include dielectric breakdown voltage, moisture content, viscosity, thermal conductivity, and flash point. Testing standards such as IEC 60156 (breakdown voltage), ASTM D877/D1816 (oil testing), and IEC 60247 (dielectric dissipation factor) are widely used to evaluate fluid health. Dissolved Gas Analysis (DGA) is another critical tool that monitors the condition of transformer oils by detecting gases produced during thermal or electrical faults.
Regular diagnostic testing allows early detection of contamination, oxidation, or moisture ingress. By tracking these values, maintenance teams can take corrective action before failures occur, extending equipment life and ensuring uninterrupted service.
Innovations – Nanofluids and Sustainability Trends
The development of nanofluids is revolutionizing dielectric technology. By suspending nanoparticles like Al₂O₃, SiO₂, or graphene in base fluids, engineers have achieved significant improvements in dielectric strength, heat transfer, and thermal stability. These advanced fluids operate under higher electrical stress while maintaining lower temperatures, leading to greater reliability and efficiency.
Sustainability trends favor the use of natural and synthetic esters due to their biodegradability, reduced greenhouse gas footprint, and compliance with modern fire safety and environmental standards. As industries shift toward eco-friendly energy solutions, insulating fluids are being optimized to deliver both performance and environmental benefits. Monitoring breakdown voltage helps evaluate the condition of dielectric fluids and ensures they can withstand high voltages.
Practical Guidance – Selection Criteria Based on Fire Safety, Environmental Regulations, Maintenance Strategy, and Transformer Design Optimization
Choosing the right fluid involves striking a balance between technical performance and safety and environmental requirements. Fire safety considerations often favour natural esters, which have much higher fire points than mineral oils. Environmental regulations are increasingly encouraging fluids with low toxicity and high biodegradability to minimize ecological risks. A maintenance strategy also plays a role; fluids with greater oxidation stability and moisture tolerance can extend maintenance intervals, thereby lowering overall operating costs. Ultimately, transformer design optimization—including heat transfer requirements, viscosity, and load profiles—may dictate which fluid type offers the best efficiency and long-term reliability. Core parts of transformer components are submerged in dielectric fluid to minimize electrical discharge and control temperature.
Frequently Asked Questions
What are the Critical Components for Industrial Electricians?
Understanding the intricacies of electrical power distribution transformers is paramount for industrial electricians. These vital components play a pivotal role in the efficient and reliable delivery of electrical power to industries and businesses worldwide. By delving into the fundamental concepts of transformer operation, types, maintenance, and future trends, industrial electricians can gain valuable insights to optimize electrical systems, troubleshoot potential issues, and ensure a reliable and uninterrupted power supply. Insulating oil is essential for preventing electric discharges in high-voltage equipment. By immersing electrical components in these fluids, manufacturers can significantly reduce the risk of arcing and short circuits. Techniques like immersion cooling utilize insulating oil to effectively dissipate heat generated by high-power components, ensuring optimal performance and longevity.
What are the key characteristics of an effective electrical insulating oil?
The primary function of electrical insulating oil is to provide electrical insulation. Filling the gaps between electrical components prevents arcing and short circuits, which can lead to equipment failure and potentially hazardous situations. Additionally, dielectric fluid excels at dissipating heat generated by electrical equipment, ensuring optimal performance and longevity.
What are the most common types of electrical insulating oil, and where are they used?
Electrical insulating oil comes in various types, each with its unique properties and applications. Historically, mineral oil has been the most commonly used dielectric fluid, offering a balance of cost-effectiveness and reliability. However, its environmental impact and susceptibility to degradation have led to the development of alternative options. Synthetic esters, for instance, provide superior dielectric properties, thermal stability, and biodegradability, making them a more environmentally friendly choice. Silicone fluids, renowned for their exceptional thermal stability and resistance to oxidation, are frequently employed in high-voltage applications where reliability and long-term performance are crucial. While perfluorinated fluids offer exceptional dielectric strength and thermal stability, their high cost and potential environmental impact limit their widespread use.
The performance of electrical insulating oil is influenced by several factors. A crucial factor is dielectric strength, which measures the fluid's ability to withstand high voltages without breaking down. Additionally, the fluid's thermal stability is essential for maintaining its insulating properties under varying temperature conditions. Chemical stability is also important, as it ensures the fluid's resistance to degradation and oxidation. Furthermore, a low flash point and flammability rating are crucial for safety, especially in enclosed environments. Lastly, the environmental impact of the fluid, including its biodegradability and toxicity, is becoming increasingly significant in the selection of dielectric fluids.
How does transformer oil impact sustainability?
Regular testing and maintenance are crucial to ensure the optimal performance of insulating oil. These tests evaluate critical properties, including dielectric strength, moisture content, and acidity level. By monitoring these parameters, engineers can identify potential issues and take corrective actions to prevent equipment failures. This proactive approach helps maintain the reliability and safety of electrical systems.
Dielectric fluid is an essential component in high-voltage electrical systems. They provide critical insulation and cooling properties, preventing electrical breakdowns and ensuring the reliable operation of equipment. By understanding the properties and applications of different dielectric fluids, engineers and technicians can select the most suitable fluid for specific applications and optimize system performance.
Related Articles
A review of the fundamental dielectric characteristics of ester-based dielectric liquids
Fundamental dielectric characteristics describe permittivity, dielectric constant, polarization, loss tangent, conductivity, and frequency response, guiding material selection, insulating performance, impedance behavior, and electric field interactions across applications in electronics, power systems, and RF design.
What Are Fundamental Dielectric Characteristics?
Material metrics like permittivity, loss tangent, and polarization that govern insulating behavior under electric fields
✅ Determines energy storage via permittivity and dielectric constant
✅ Quantifies dissipation with loss tangent and conductivity
✅ Captures frequency response, polarization, and dielectric breakdown
1. Introduction
For many years synthetic ester fluids were seen as specialist materials, only for use in unusual transformers, such as those in rolling stock, offshore installations and steel plants where fire safety was a prime consideration. However, in more recent times users are realizing that ester-based liquids could offer a more mainstream alternative to mineral oil and although these fluids are more expensive the overall project costs can be lower when taking into account factors such as reduced fire protection. In some space-constrained urban environments ester-based liquids may even become the preferred option, with the flammability and potential environmental impact of mineral oil making the design of modern installations extremely challenging. This type of situation has been seen with the latest 400kV projects incorporating synthetic ester fluids. For context, readers can review the fundamentals of dielectric fluids to understand how base chemistry influences flammability and environmental performance.
2. Standard AC Breakdown Testing
Standard test methods for assessing breakdown voltage of liquids typically employ small electrode gaps, of the order of ≤2.54mm. The electrode configuration can vary from spherical, through VDE type “mushroom” electrodes to disc electrodes. This type of testing is primarily used to give an evaluation of the cleanliness of a liquid since it gives very limited information about the actual dielectric performance. It can be seen by comparing the results in Table 1 that all the different types of liquids to be discussed in this paper give very similar results for a given electrode arrangement in this type of testing. Clarifying the definition of breakdown voltage in insulating oil helps interpret these short-gap results.
This could lead to the conclusion that all these liquids are equal in their dielectric performance, or that given a good result in the AC breakdown test one liquid is in some way superior to another. However, the true picture is more complex, since the electrical stress distribution is influenced by many factors such as electrode geometry, distance and materials types. Another key factor in the dielectric behavior is the wave shape of the applied voltage. AC voltage in the form of a clean sine wave is usually expected at frequencies of 50-60Hz depending on the geographical location. However, this is rarely the case with harmonics and other distortions of the pure waveform. In addition the prevalence of surges on the network must be accounted for; in testing this is usually characterized by two different types of event, either lightning surge or switching surge and there are standard waveforms established to test these.
In practice, understanding how oil in transformers behaves under distorted waveforms informs appropriate test selection.
So any dielectric system in a transformer must withstand AC conditions, switching impulse and lightning impulse, as well as chopped lightning impulse if this is specified. There may also be a requirement to withstand DC fields in some special cases and this adds an extra level of complexity.
When considering a new dielectric medium, therefore, all these aspects need to be tested and in the beginning researchers will look to comparisons with existing materials of known behavior to assess likely changes. As stated previously in terms of short gap AC behavior ester-based liquids are very similar to mineral oil and this gives some confidence that they can be used. For distribution class equipment up to 33kV the change to ester has required little in the way of detailed electrical design evaluation, since the electrical margins are large due to the need for excess solid insulation to provide mechanical strength. However as the voltage level rises there is less electrical margin and the need for routine impulse testing, both of which mean that greater steps are needed to evaluate design. So to begin using ester-based liquids in power class transformers there is a need to check impulse behavior over similarly short gaps to the AC tests, and this is where see some differences start to emerge.
Complementary programs of transformer oil analysis can track moisture, particles, and aging markers that strongly influence PD and impulse withstand.
3. Impulse Strength of Short Electrode Gaps
There are standard methods for measuring impulse breakdown with the ASTM D3300 being one popular method. The electrode arrangement for this test can be either needle to sphere, or sphere to sphere. In the first instance researchers started work with small electrode gaps employing a sphere-sphere set up, such as the example in Fig 1. utilized by the University of Manchester.
Fig.1. Arrangement for short gap impulse tests
In their testing, a number of different methods were applied for stepping up the test voltage, following the recommendations in different standards. This showed a lower impulse breakdown strength for the ester liquids and Fig 2. shows a summary of the results, with the maximum difference in breakdown voltage being of the order of 20%. In this case the mineral oil tested was Nynas Nytro Gemini X, the synthetic ester M&I Materials MIDEL 7131 and natural ester Cargill Envirotemp FR3. These observations are consistent with broader properties of transformer insulating oil related to ionization, space charge, and pre-breakdown dynamics.
Fig. 2. Results of impulse breakdown testing to various methods
4. Partial Discharge Inception
To further understand the mechanism behind the different behavior that was observed, researchers started looking at very divergent arrangements, for example a sharp needle of tip radius 6.5µm and sphere of radius 12.5mm, as this allows observation of phenomena in a liquid with manageable voltage levels.[3] This allowed the study of partial discharge inception, when the liquid begins to yield to the electrical field. When the researchers subjected this arrangement to AC they discovered that the PDIV of ester-based liquids with a gap of 50mm is actually very close to that of mineral oil.
In fact in the case of natural ester a higher PDIV was found than in mineral oil. This suggested that the reason for the difference in impulse breakdown behavior does not lie in discharge inception, although some different behavior was found in this study, especially in polarity, between mineral oil and esters. Mineral oil exhibits a very strong tendency to PD only in the positive half cycle of the AC waveform, i.e. when the needle is at a positive polarity. In the negative half cycle the required voltage to form PD is much higher than that of the PDIV. In the ester-based liquids the situation is somewhat different; PD was found in the negative half cycle at much closer voltages to the positive half cycle PDIV, as shown Fig. 3.
Fig. 3. PDIV in positive (left hand chart) and negative (right hand chart) half cycles
This indicated that the electrical behavior is not the same between the liquid types. It also throws up questions around the way mineral oil filled transformers are tested, i.e. is only testing with negative impulse a valid practice?
5. Streamer Propagation Behavior
The similarity in PDIV between esters and mineral oil required a closer look at propagation of electrical discharges. The next important step was then to look at the discharge channels in the liquids, known as streamers. This involved the combined techniques of electric measurement and visual imaging to detect how streamers form in liquids and how they propagate. Much of this work was conducted in parallel in different research institutions,where the same conclusion was drawn. Streamer propagation in esters is different to mineral oil, especially under very divergent fields, such as those the researchers were using. The key conclusion from this was a difference in so-called acceleration voltage when streamers move from slow mode propagation to fast mode.
In order for a flashover to occur it is necessary for the electrical current to find a path from one electrode to another and in liquids this occurs within a gaseous channel, known as a streamer. This channel will only propagate through the fluid if it has sufficient field strength to provide motive force and sufficient time. When considering AC behavior the time is relatively long, whereas under impulse conditions the time is extremely short. The standard wave shape for lightning impulse has a rise time of 1.2µs and fall time of 50µs to reach 50% of maximum. This means that the peak electrical field is only present for a matter of micro-seconds and in order to get propagation from one electrode to another, especially over longer oil gaps, the discharge must attain a high velocity. Streamers can be characterized by four different modes, as shown in Fig. 4.
Fig. 4. Streamer velocities and modes
The principle behind the connection between streamer mode and breakdown can be demonstrated with a simplified example. Taking a gap size of 50mm, if it is assumed that the liquid is only subjected to the voltage necessary to sustain propagation for 5µs then the streamer will need to attain a velocity of 10km/s or in other words be of Mode 3-4 to bridge the gap and cause a breakdown. Otherwise the streamer will only be characterised as a partial discharge. The transition from Mode 1/2 to Mode 3/4 can be characterised as the acceleration voltage.
A variety of researchers have looked at the acceleration voltage principle with esters and all agree that this is one area where these liquids differ from mineral oil. The charts in Fig. 5. show the behavior when the electrode system is extremely divergent, with esters having a substantially lower acceleration voltage than mineral oil, especially under positive polarity.
Fig. 5. Acceleration voltage under Positive polarity and Negative polarity at 50mm spacing
6. Testing with More Realistic Electrode Arrangements
Although this difference in acceleration voltage would appear to prevent the use of esters at higher voltages as the electrode arrangement becomes less divergent, inception begins to become more important for the withstand level. This supports the findings of researchers who have studied the behavior with varying levels of divergence in the electrodes, from homogenous through to highly divergent.
When thinking about the design of real world equipment and transformers for transmission levels, the more homogeneous case actually represents the majority of the configurations to be considered. Needle to plate type situations are avoided as part of good design and manufacturing, as it is known that these are electrically weak and prone to producing discharges. Consequently, criteria for selecting oil for transformers should consider field uniformity, surge exposure, and insulation geometry as well as fire safety.
Research looking at impulse behavior under more realistic arrangements has focussed on tap changer contacts, since these represent a more divergent part of power transformer designs. In this case the arrangement shown in Fig. 6. was used and the results obtained under impulse conditions showed very little difference between ester and mineral oil.
Fig. 6. Tap changer contacts used for natural ester evaluation
Fig. 7. shows the Weibull distribution for results obtained in this arrangement. This gives some confidence that even though the situation with a needle and plate looks unfavourable, as soon as the configuration starts to reflect the real world situation, the difference between esters and mineral oil becomes much smaller.
Fig. 7. Weibull distribution of lightning impulse breakdown under positive polarity
7. Laboratory Testing of Creepage Discharge and Flashover
Another area where divergence becomes important is over long creepage paths, where there is effectively a concentrated area of electrical field at one end, with a very long distance to the lower potential. A popular form of arrangement for testing creepage behavior is the so-called Weidmann set up, of a paper-wrapped or bare conductor in contact with a pressboard barrier, as shown in Fig 8.
Fig. 8. Weidmann electrode arrangement
When this type of arrangement has been tested over gap sizes up to 35mm it has been found that esters give similar flashover results to mineral oil, as shown in Table 3. The difference between the liquids in this arrangement is small - not even as large as that found in small oil gaps. This suggests that even though design modification may be necessary, there is not the very large difference that might be assumed if the acceleration voltage in extremely divergent set up was used.
8. Testing in Prototype Transformers
Another area where more focus may be required with an ester based liquid is over very long creepage paths far beyond the distances tested with the Weidmann arrangement, since the fundamental investigations indicate that propagation is key. Experience from real transformer prototypes has shown that failure modes over extremely long paths support the faster propagation model. Researchers from Brazil found that when testing a single phase 245kV prototype transformer, in natural ester, designed to mineral oil rules, the natural ester failed at 100% of Basic Insulation Level (BIL) rating, when tested with lightning impulse along a long gap discharge path, as shown in Fig.
3. This unit had an HV winding with a center connection coil.
Fig. 9. Model of winding showing discharge path
The designers of this transformer noted that although they experienced this failure it does not prevent the use of esters at higher voltage. However, there may need to be more design margin and closer attention paid to peak stress areas and long creepage paths. Thermal design and transformer cooling also affect viscosity and bubble formation, which in turn impact dielectric margins at high stress.
This is a theme that is often mentioned in the industry when discussing ester-based liquids and the necessary design changes. It is important to note that a growing number of manufacturers have carried out their own research in addition to the published works; to date there are a number of transformers successfully operating at 400kV+ with esters. There are also many other projects in development, and the expectation is that in the coming years esters will move from a being a product used in niche applications to one deployed in mainstream installations.
9. Conclusions
Over the last fifteen years a great deal of research has been conducted into understanding the electrical behavior of ester-based liquids, under a range of different conditions. This has been driven by a desire for safer, more environmentally friendly transformers.
The laboratory based test arrangements with extremely divergent fields indicate a difference in the streamer propagation behavior between esters and mineral oil, which may mean designers need to pay attention to certain portions of the dielectric structure. Evaluations with more realistic electrode arrangements indicate that although there is a difference in behavior, this will not prevent the use of esters at higher voltages. The experience in real world applications, where esters are now utilized for power transformers for 400kV+ also supports this assertion.
The key aspects for designers when considering ester-based liquids are to design a discharge-free transformer; extra margin may be needed over long creepage paths and in divergent arrangements to compensate for the higher probability of propagation. This could be summarized by saying that with mineral oil, discharges may occur, without flashover, but in ester there is a higher probability of discharge becoming breakdown.
Related Articles
Advancements in Dissolved Gas Analysis Explained
Advancements in dissolved gas analysis2 deliver smarter transformer condition monitoring, predictive maintenance, and fault diagnostics via online sensors, IEC 60599 methods, Duval Triangle analytics, and machine learning for grid reliability.
What Are Advancements in Dissolved Gas Analysis2?
Modern DGA methods using online sensors, IEC standards, and AI to diagnose transformer faults proactively.
✅ Real-time gas monitoring via online chromatographs and sensors
✅ AI and Duval Triangle enhance fault classification accuracy
✅ Standards-based analysis per IEC 60599 supports maintenance
One of the most important steps when looking at DGA data is to decide whether the data support the existence of a fault that is actively breaking down the insulation before you try to use a triangle, pentagon, or gas ratio method to identify a fault type. Otherwise, you are diagnosing random measurement noise, not the transformer. Conventional methods assign limits to each of the gases to detect and assess abnormal gas formation. Formerly it was common practice to add gas concentrations together to get total dissolved combustible gas (TDCG). The hope was to simplify the task of detecting abnormal gas production and interpreting rates of change. This, however, was equivalent to counting U.S. Dollars, Mexican Pesos, Bitcoins, and Canadian Loonies and thinking that the sum represented “value”. To reduce false positives from sensor drift and sampling errors, recent work on advancements in DGA data quality outlines practical controls for sampling, calibration, and trending.
Electrical Transformer Maintenance Training
Substation Maintenance Training
Request a Free Training Quotation
Chemistry dictates that each gas we observe requires a different amount of energy to break away from the original insulating material. Instead of trying to interpret several individual gas concentrations, why not follow the energy associated with the gassing? The energies required to form the gas can be weighted by the gas concentrations and added up.
For a grounding in principles and typical fault signatures, see this overview of dissolved gas analysis techniques and their diagnostic use.
This idea of using standard heats of formation of fault gases for DGA was worked out in Jakob et al. 2012 and demonstrated to be an improvement compared to TDCG and other gas concentration sums. Soon after that, chemist Fredi Jakob realized that it would be better to create a fault energy index, which he called normalized energy intensity (NEI), to represent the influence of an internal fault on the insulating oil. That idea was presented in Jakob & Dukarm 2015, where it was shown that NEI was very useful for trending fault severity and not partial to any particular fault types. The figure illustrates how trending cumulative NEI simpli.es the detection of suspicious gas production. For additional context on modern interpretation frameworks, review these advancements in dissolved gas analysis that compare energy-based indices with classical ratio methods.
NEI, now renamed NEI-HC, is based on the low molecular weight hydrocarbon gases generated from cracking mineral oil. Another fault energy index, called NEI-CO, is based on the carbon oxide gases formed by pyrolysis of cellulose in paper insulation. The formulas for NEI-HC and NEI-CO are shown in Equations (1) and (2) below. Since each set of gases comes from a different insulation material, you can assess and track which faults are affecting paper, hot metal in the oil, or both. That knowledge can help point to the root cause and better estimate the severity of the problem. When paper degradation is suspected, trends can be corroborated with guidance on the CO/CO2 ratio in DGA to strengthen evidence for thermal versus oxidative effects.
Because NEI-HC derives from oil cracking, selecting and maintaining a high-quality transformer insulating oil is essential for resilient performance under thermal stress.
NEI-HC = 77.7[CH4] + 93.5[C2H6] + 104.1[C2H4] + 278.3[C2H2] / 22400 (1)
NEI-CO = 101.4[CO] + 30.19[CO2] / 22400 (2)
The highest heat of formation for the hydrocarbons is C2H2 and for carbon oxides it is CO. This physically confirms the general intuition that these gases are the most concerning to see in transformer DGA. These concerns underscore why routine transformer oil analysis remains central to risk-based maintenance planning.
You can trend fault energy indices to identify gassing episodes and relate them to external events such as through faults, maintenance work orders, and load changes to help determine what might have triggered the gassing. Also, you can track the cumulative energy over the history of the transformer to counteract effects of gas-loss (see previous article in this series). Interpreting those trends alongside the unit's fundamental dielectric characteristics helps differentiate benign load-related gassing from insulation distress.
Related Articles
Transformer Cooling
Transformer cooling enhances thermal management via oil-immersed and air-cooled systems, radiators, fans, and pumps. Methods like ONAN, ONAF, and OFAF reduce temperature rise, limit insulation aging, and improve efficiency under varying load.
What Is Transformer Cooling?
Transformer cooling removes heat from windings and core via oil or air circulation to control temperature and slow aging.
✅ Common types: ONAN, ONAF, OFAF, OFWF for various ratings.
✅ Components: radiators, fans, oil pumps, heat exchangers.
✅ Benefits: lower temperature rise, higher efficiency, longer life.
A little energy lost in a transformer must be dissipated as heat. Although this energy is but a small portion of the total energy undergoing transformation, it becomes quite large in amount in transformers of larger kVA ratings. To maintain efficiency and life expectancy the transformer's cooling system needs to be operating at peak performance. For dry-type transformers, the ventilation system of the room should be inspected to make sure it is operating efficiently. For forced air-cooled systems, the fan motors should be checked for proper lubrication and operation. Water-cooled systems must be tested for leaks and proper operation of pumps, pressure gauges, temperature gauges and alarm systems.
In liquid-filled designs, the choice and maintenance of oil in transformers directly influence heat removal performance and long-term reliability.
When a liquid coolant is used its dielectric should be tested. Water in the coolant will reduce its dielectric strength and the insulation quality. In cases where the dielectric strength of the coolant is reduced significantly, conducting arcs may develop causing short-circuits when the transformer is energized. A standard oil dielectric test involves applying high voltage to a sample taken from the transformer and recording the voltage at which the oil breaks down. If the average breakdown voltage is less than 20 kilovolts, the oil will need to be filtered until a minimum average breakdown of 25 kilovolts is achieved. Technicians often reference breakdown voltage of oil guidelines to interpret test results and schedule remediation.
Comprehensive transformer oil analysis can reveal moisture ingress, dissolved gases, and particulate contamination before failures occur.
Oil-insulated transformers use mineral oil for cooling. This oil is thin enough to circulate freely and does a good job of providing insulation between the transformer windings and the core. It is however subject to oxidation and if any moisture enters the oil, its insulating value is substantially reduced. In addition, mineral oil is flammable and therefore should not be located near combustible materials indoors or outdoors. In critical applications, selecting a high-quality transformer insulating oil mitigates oxidation, moisture effects, and thermal aging.
These behaviors align with the fundamental dielectric characteristics that govern insulation performance under electrical and thermal stress.
There are several types of transformer oil cooling solutions:
- oil air
- forced oil
- oils water
- oil natural
- air forced
- heated oil
- oil forced
- natural
In practice, each configuration must be evaluated alongside the properties of the chosen dielectric fluid to balance cooling effectiveness, safety, and service life.
Outdoor liquid-cooled transformers usually use mineral oil, and liquid cooled transformers for inside use are filled with a synthetic liquid that is nonflammable and nonexplosive. Synthetic oil coolants must be handled with care as they sometimes cause skin irritations. One type, askarelinsulated transformers used in past years contained polychlorinated biphenyls (PCBs), which are known to cause cancer. Askarel has been banned by the Environmental Protection Agency and its use as a transformer coolant is being phased out. However, askarel coolants are still found throughout the electrical industry in older transformers and direct contact with them should be avoided. The NEC still contains provisions for installing askarel transformers. The following is a list of the different types of liquid-filled transformers recognized by the NEC:
Facility engineers should review application requirements, fire codes, and material compatibility when selecting oil for transformers to ensure compliance and dependable operation.
- Oil-Insulated--uses chemically untreated insulating oil
- Askarel—uses nonflammable insulating oil
- Less-Flammable Liquid-Insulated--uses reduced flammable insulating oil
- Nonflammable Fluid-Insulated--uses noncombustible liquid