Latest Overhead T&D Articles

Overhead T&D, Direct Current Technology

Direct current technology delivers efficient DC power distribution via rectifiers, converters, and power electronics, enabling microgrids, energy storage, HVDC links, photovoltaics, and electric vehicle charging with reduced losses and improved reliability.

 

What Is Direct Current Technology?

Direct current technology uses one-way flow and power electronics to enable efficient DC distribution and control.

✅ Unidirectional conduction for stable voltage and reduced conversion losses

✅ Power electronics: rectifiers, DC-DC converters, inverters, protection

✅ Applications: HVDC links, microgrids, EV charging, PV and battery systems

 

Direct current (DC) is the preferred technology for moving large amounts of power across long distances. DC results in overall higher efficiency and reliability than an equivalently-sized alternating current (AC) system moving the same amount of power.

The Advantages of DC

More efficient: Over long distances, DC transmission can move more power with less electrical losses than an equivalent AC transmission line. For foundational context on grid-scale power flows, see electricity transmission basics to understand how DC and AC corridors are planned.

Lower Cost: Higher efficiency means a lower transmission cost, helping renewable energy compete against other power sources. Advances in overhead switchgear innovation can also drive capital and operating savings across long routes.

Improved Reliability: HVDC transmission can enhance system stability, allow the operator complete control over power flow, and facilitate the integration of wind from different resource areas. These characteristics align with smart grid strategies that require precise controllability and resilience.

Smaller Footprint: DC transmission lines require narrower right-of-way footprints, using less land, than equivalent AC lines. Planning and design of overhead transmission lines further influence corridor width, clearances, and visual profile.

The major advantage of DC power lines is their efficiency—less energy is lost as it is transmitted and there is no need for reactive compensation along the line. Because DC (Direct Current) flows steadily through the wires without changing direction many times each second and through the entire conductor rather than at the surface, DC (Direct Current) transmission lines typically lose less power than AC transmission lines. By comparison, AC transmission lines must manage reactive power and frequency-related effects over distance.

How HVDC Works

Historically, the transfer of electricity between regions of the United States has been over high voltage alternating current (AC) transmission lines, which means that both the voltage and the current on these lines move in a wave-like pattern along the lines and are continually changing direction.  In North America, this change in direction occurs 60 times per second (defined as 60 hertz [Hz]).  The electric power transmitted over AC transmission lines is exactly the same as the power we use every day from AC outlets, but at a much higher voltage. From bulk transmission, electrical distribution systems step and route energy to neighborhoods and facilities.

Unlike an AC transmission line, the voltage and current on a direct current (DC) transmission line are not time varying, meaning they do not change direction as energy is transmitted.  DC electricity is the constant, zero-frequency movement of electrons from an area of negative (-) charge to an area of positive (+) charge.

The first commercial electric power system built by Thomas Edison in the late nineteenth century carried DC electricity, but given some early advantages, AC power eventually became the primary power system in the United States.  Some of these advantages are no longer applicable (e.g., technology has advanced to allow efficient conversion from AC to DC), and DC transmission is the preferred solution for moving large amounts of renewable power over long distances.

Clean Line’s HVDC transmission lines projects will deliver power from new, renewable energy resources.  These resources will be AC generators, as is normally the case, and their energy will be transmitted along collector lines.  These collector lines will then be connected to a substation where the power will be collected and the voltage will be transformed from the voltage of the collector lines to a common voltage (such as 345,000 volts).  The power will then be converted to DC, a process known as rectification, using power electronic switches called thyristors.  The power will then be transmitted several hundred miles along a set of conductors called a transmission line before getting converted back to AC, a process known as inversion, again using thyristors as the switching devices.  After the DC power is converted back to AC it is transformed to the common voltage of the grid to which it is being connected (e.g. 500,000 volts or 765,000 volts, in the case of Clean Line’s projects).  This power is then distributed via the interconnected grid by the local utilities to homes and businesses.  See below for an illustration of this process.
  Once inverted and synchronized, the power enters local power distribution for last-mile delivery and metering.

The History of DC Transmission

The development of direct current (DC) transmission dates back to the 1930’s and has been a proven technology since the first major installations in 1954.  Over the last 40+ years, DC Projects have shown to offer significant electrical, economic, and environmental advantages when transporting power across long distances, where there has been a veritable boom in the use of DC to tap energy resources in remote portions of the country and bring the energy to consumers in more heavily populated areas.  Among those direct current lines is the Pacific DC Intertie, which has been in operation for over 30 years.  Operating at ±500 kilovolts, the line is capable of transmitting up to 3,100 MW of power.  In terms of operating voltage and capacity, the Pacific Intertie is similar to the Clean Line transmission line projects, which will operate at ±600 kilovolts and deliver up to 3,500 MW of power.

Currently there are more than 20 DC transmission facilities in the United States and more than 35 across the North American grid.

 

Related Articles

View more

Sign Up for Electricity Forum’s Overhead T&D Newsletter

Stay informed with our FREE Overhead T&D Newsletter — get the latest news, breakthrough technologies, and expert insights, delivered straight to your inbox.

High Voltage AC Transmission Lines

Ac transmission lines deliver alternating current across the power grid using high voltage, overhead conductors, and insulators, controlling reactive power, impedance, and corona effects to minimize losses, improve efficiency, and ensure reliable long-distance electricity transmission.

 

What Are AC Transmission Lines?

Ac transmission lines carry high-voltage AC power long distances with minimal losses.

✅ Typical voltages: 69 kV to 765 kV; higher reduces I2R losses

✅ Requires reactive power compensation: shunt capacitors, SVC, STATCOM

✅ Design factors: conductor bundling, corona control, insulation coordination

 

Three-phase electric power systems are used for high and extra-high voltage AC transmission lines (50kV and above). The pylons must therefore be designed to carry three (or multiples of three) conductors. The towers are usually steel lattices or trusses (wooden structures are used in Germany in exceptional cases) and the insulators are generally glass discs assembled in strings whose length is dependent on the line voltage and environmental conditions. One or two earth conductors (alternative term: ground conductors) for lightning protection are often added to the top of each pylon. For background on material properties, the electrical insulator overview provides relevant design considerations.

Detail of the insulators (the vertical string of discs) and conductor vibration dampers (the weights attached directly to the cables) on a 275,000 volt suspension pylon near Thornbury, South Gloucestershire, England. In some countries, pylons for high and extra-high voltage are usually designed to carry two or more electric circuits. For double circuit lines in Germany, the “Danube” towers or more rarely, the “fir tree” towers, are usually used. If a line is constructed using pylons designed to carry several circuits, it is not necessary to install all the circuits at the time of construction. Medium voltage circuits are often erected on the same pylons as 110 kV lines. Paralleling circuits of 380 kV, 220 kV and 110 kV-lines on the same pylons is common. Sometimes, especially with 110 kV-circuits, a parallel circuit carries traction lines for railway electrification. Additional context on span lengths, conductor bundles, and right of way is covered in this transmission lines reference for practitioners.

High Voltage DC Transmission Pylons

High voltage direct current (HVDC) transmission lines are either monopolar or bipolar systems. With bipolar systems a conductor arrangement with one conductor on each side of the pylon is used. For single-pole HVDC transmission with ground return, pylons with only one conductor cable can be used. In many cases, however, the pylons are designed for later conversion to a two-pole system. In these cases, conductor cables are installed on both sides of the pylon for mechanical reasons. Until the second pole is needed, it is either grounded, or joined in parallel with the pole in use. In the latter case, the line from the converter station to the earthing (grounding) electrode is built as underground cable. Engineers can review converter topologies, pole configurations, and control methods in the direct current technology guide to inform design choices.

Guidance on electrode placement, resistivity, and corrosion protection is summarized in the grounding electrodes overview relevant to HVDC return paths.

Raliway Traction Line Pylons

Pylons used for single-phase AC railway traction lines are similar in construction to pylons used for 110 kV-three phase lines. Steel tube or concrete poles are also often used for these lines. However, railway traction current systems are two-pole AC systems, so traction lines are designed for two conductors (or multiples of two, usually four, eight, or twelve). As a rule, the pylons of railway traction lines carry two electric circuits, so they have four conductors. These are usually arranged on one level, whereby each circuit occupies one half of the crossarm. For four traction circuits the arrangement of the conductors is in two-levels and for six electric circuits the arrangement of the conductors is in three levels. With limited space conditions, it is possible to arrange the conductors of one traction circuit in two levels. Running a traction power line parallel to high-voltage transmission lines for threephase AC on a separate crossarm of the same pylons is possible. If traction lines are led parallel to 380 kV-lines, the insulation must be designed for 220 kV because, in the event of a fault, dangerous overvoltages to the three-phase alternating current line can occur. Traction lines are usually equipped with one earth conductor. In Austria, on some traction circuits, two earth conductors are used. Integration with substation feeders and sectioning posts must align with the power distribution practices used along the route.

Types Of Pylons

Specific Functions:

  • anchor pylons (or strainer pylons) utilize horizontal insulators and occur at the endpoints of conductors.
  • pine pylon – an electricity pylon for two circuits of three-phase AC current, at which the conductors are arranged in three levels. In pine pylons, the lowest crossbar has a wider span than that in the middle and this one a larger span than that on the top.
  • Twisting pylons are anchor pylons at which the conductors are “twisted” so that they exchange sides of the pylon.
  • long distance anchor pylon

A long distance anchor pylon is an anchor pylon at the end of a line section with a long span. Large gaps between pylons reduces the restraints on the movement of the attached conductors. In such situations, conductors may be able to swing into contact with each during high wind, potentially creating a short circuit. Long distance anchor pylons must be very stably built due to the large weight of the exceptionally long cables. They are implemented occasionally as portal pylons. In extreme cases, long distance anchor pylons are constructed in pairs, each supporting only a single cable, in an effort to reduce the strain of large spans.

Branch Pylon: In the layout of an overhead electrical transmission system, a branch pylon denotes a pylon which is used to start a line branch. The branch pylon is responsible for holding up both the main-line and the start of the branch line, and must be structured so as to resist forces from both lines. Branch pylons frequently, but not always, have one or more cross beams transverse to the direction of travel of the line for the admission of the branching electric circuits. There are also branch pylons where the cross beams of the branching electric circuits lie in the direction of travel of the main line. Branch pylons without additional cross beams are occasionally constructed. Branch pylons are nearly always anchor pylons (as they normally must ground the forces from the branch line). Branch pylons are often constructed similarly to final pylons; however, at a branch pylon the overhead line resumes in both directions, as opposed to only one direction as with a final pylon.

 Anchor Portal: An anchor portal is a support structure for overhead electrical power transmission lines in the form of a portal for the installation of the lines in a switchyard. Anchor portals are almost always steel-tube or steel-framework constructions.

 Termination Pylon: Anchor pylons or strainer pylons utilize horizontal insulators and occur at the endpoints of conductors. Such endpoints are necessary when interfacing with other modes of power transmission (see image) and, due to the inflexibility of the conductors, when significantly altering the direction of the pylon chain. Anchor pylons are also employed at branch points as branch pylons and must occur at a maximum interval of 5 km, due to technical limitations on conductor length. Conductors are connected at such pylons by a short conductor cable “strained” between both ends. They often require anchor cables to compensate for the asymmetric attachment of the conductors. Therefore, anchor pylons tend to be more stably built than a support pylon and are often used, particularly in older construction, when the power line must cross a large gap, such as a railway line, river, or valley. A special kind of an anchor pylon is a termination pylon. It is used for the transition of an overhead powerline to an underground cable. A termination pylon at which the powerline runs further as well as overhead line and as underground cable is a branch pylon for a cable branch. For voltages below 30kV, pylon transformers are also used. Twisted pylons are anchor pylons at which the conductors are “twisted” so that they exchange sides of the pylon. Anchor pylons may also have a circuit breaker attached to their crossbeam. These so called switch pylons are operated from the ground by the use of long sticks. The attachment of circuit breakers to pylons is only practical when voltages are less than 50kV. Where sectionalizing or protection is required aloft, utilities are adopting overhead switchgear innovations to reduce footprint and maintenance.

Materials Used

  • Wood Pylon
  • Concrete Pylon
  • Steel Tube Pylon
  • Lattice Steel Pylon

Conductor Arrangements

Portal Pylon: In electricity distribution, a portal pylon is a type of pylon with which the cross beams on the conductor cables rest on at least two towers. Portal pylons can be made of wood, concrete, steel tubing or steel lattice. They are used in German railroad wiring because of their enormous space requirement as a rule only for anchor pylons, which have to resist high traction power and as bases for lines in switchgears as anchor portals. Their application and clearances are coordinated with prevailing electrical distribution systems standards for safe operation.

Delta Pylon: A delta pylon is a type of support structure for high-voltage electric power transmission lines. The pylon has a V-shapedtop for the admission of the cross beam. Delta pylons are usually established only for one electric circuit, occasionally for two electric circuits. They are used for voltages up to 765 kV. Delta pylons are far more common in the USA, France, Spain, Italy and formerYugoslavia, while in Germany on delta pylons shifted high voltage transmission lines are very rare.

Single-level Pylon: A single-level pylon is an electricity pylon for an arrangement of all conductor cables on a pylon in one level. The singlelevel pylon leads to a low height of the pylons, connected with the requirement for a large right of way. It is nearly always used for overhead lines for high-voltage direct current transmissions and traction current lines. If three-phase current is used, if the height of pylons may not exceed a certain value.

Two-level Pylon: A two-level pylon is a pylon at which the circuits are arranged in two levels on two crossbars. Two-level pylons are usually designed to carry four conductors on the lowest crossbar and two conductors at the upper crossbar, but there are also other variants, e.g. carrying six conductors in each level or two conductors on the lowest and four on the upper crossbar. Two-level pylons are commonplace in former West-Germany, and are also called Donau pylons after the river Danube.

Three-level Pylon: A three-level pylon is a pylon designed to arrange conductor cables on three crossbars in three levels. For two three-phase circuits (6 conductor cables), it is usual to use fir tree pylons and barrel pylons. Three-level pylons are taller than other pylon types, but require only a small right-of-way. They are very popular in a number of countries.

Three-level Pylon: A three-level pylon is a pylon designed to arrange conductor cables on three crossbars in three levels. For two three-phase circuits (6 conductor cables), it is usual to use fir tree pylons and barrel pylons. Three-level pylons are taller than other pylon types, but require only a small right-of-way. They are very popular in a number of countries.

From: Overhead and Underground T&D Handbook, Volume 1, The Electricity Forum

 

Related Articles

View more

Grounding Electrode

A grounding electrode is a conductive element, such as a metal rod or plate, that connects electrical systems to the earth. It safely disperses fault currents, stabilizes voltage levels, and is essential for electrical safety and code compliance.

 

What is a Grounding Electrode?

A grounding electrode is a vital component of any electrical system. It is a conductive element, such as a metal rod, plate, or concrete-encased rebar, that connects the electrical system to the earth.

✅ Connects electrical systems to earth to safely discharge fault currents

✅ Helps stabilize voltage and prevent equipment damage

✅ Required for electrical code compliance and personal safety

This connection safely dissipates fault currents, stabilizes voltage levels, and protects both equipment and personnel. Proper grounding is not only essential for electrical safety but is also mandated by national electrical coA grounding electrode is a vital component of any electrical system. It is a conductive element, such as a metal rod, plate, or concrete-encased rebar, that connects the electrical system to the earth. des such as NEC 250.52 and CSA standards. To better understand the broader framework behind safe grounding practices, see our overview of electrical grounding principles.

 

NEC-Approved Grounding Electrode Types

The National Electrical Code (NEC) outlines various types of grounding electrodes approved for use in electrical installations. These include metal underground water pipes, building steel embedded in concrete, concrete-encased electrodes (commonly referred to as Ufer grounds), ground rings, and rods or pipes driven into the earth. These different electrode types are chosen based on the installation environment and desired longevity.

  • Metal water pipes must be in contact with earth for at least 10 feet.

  • Concrete-encased electrodes use rebar or copper conductor at least 20 feet in length.

  • Ground rods and pipes must be at least 8 feet long and meet diameter standards.

NEC standards such as grounding and bonding requirements are essential for selecting compliant materials and configurations.

 

Grounding Electrode Conductor (GEC) Sizing and Function

Beyond the electrode itself, the grounding electrode conductor (GEC) plays a critical role in the overall grounding system. The GEC connects the electrode to the main service panel or system grounding point. Sizing of the GEC is determined by the largest ungrounded service-entrance conductor, as outlined in NEC Table 250.66. The conductor must be adequately sized to carry fault current safely without excessive heating or damage.

  • Copper GECs typically range from 8 AWG to 3/0 AWG, depending on the system size.

  • Aluminum conductors may be used but require larger sizes due to lower conductivity.

  • For rod, pipe, or plate electrodes, the maximum required GEC size is 6 AWG copper.

Learn how proper grounding electrode conductor sizing ensures the safe dissipation of fault currents in compliance with NEC 250.66.

 

Best Practices for Ground Rod Installation

Installation best practices ensure that the electrode system performs as intended. Ground rods must be driven at least 8 feet into the soil, and if multiple rods are required, they must be spaced at least 6 feet apart. Soil conditions, moisture levels, and temperature significantly impact the effectiveness of grounding systems, making proper placement and testing crucial.

  • Electrodes should be installed vertically, where possible, for better conductivity.

  • Ground resistance testing should confirm values below 25 ohms for single rods.

  • Supplemental electrodes may be required to meet code if resistance exceeds this limit.

For deeper insight into how grounding integrates into entire system design, explore our guide on grounding systems and layout strategies.

 

Soil Resistivity and Its Impact on Grounding System Performance

Soil composition is a critical factor in determining the effectiveness of a grounding electrode. High-resistivity soils such as sand or gravel reduce system reliability. In such cases, chemical ground rods or deeper electrode systems may be required. Soil resistivity testing, using methods like the Wenner or Schlumberger test, can guide engineering decisions.

  • Moist, loamy soil provides the best conductivity.

  • Dry or frozen soil increases resistance significantly.

  • Chemical rods are useful in rocky or high-resistance soils.

If you're working in areas with soil that inhibits conductivity, high-resistance grounding methods may be necessary to maintain performance.

 

Comparing Types of Ground Rods and Their Applications

There are several types of ground rods available, each with unique properties and applications. Hot-dip galvanized rods are cost-effective and provide reliable performance in many environments. Copper-clad rods, while more expensive, offer enhanced corrosion resistance. Stainless steel and chemical ground rods are typically reserved for specialized applications with extreme soil conditions or longevity requirements.

  • Galvanized rods are economical and meet ASTM A-123 or B-633 standards.

  • Copper-clad rods meet UL 467 and offer superior corrosion protection.

  • Stainless steel and chemical rods are high-cost but high-performance options.

For clarification on the term itself, see our complete definition of electrical grounding and how it applies across systems.

 

Ensuring Electrical Code Compliance

Code compliance and product specification are essential aspects of grounding design. All rods and connectors must meet standards such as UL 467, ASTM A-123, or CSA. Installers must ensure that products ordered match specifications to avoid liabilities and safety risks. Dissimilar metals should be avoided to prevent galvanic corrosion, which can reduce system lifespan.

  • Ensure product labeling matches listed standards.

  • Avoid mixing copper and galvanized steel in close proximity.

  • Confirm resistance-to-ground targets as part of final inspection.

 

Grounding System Design for Safety and Reliability

In conclusion, designing and installing an effective grounding electrode system requires a comprehensive understanding of codes, soil science, material properties, and safety considerations. Proper selection and installation of grounding components not only ensure regulatory compliance but also promote system reliability and long-term protection of assets and personnel. Additional techniques and requirements are explained in our article on understanding electrical grounding, which connects grounding electrodes to broader system safety.

 

Related Articles

 

View more

Reliability & Protection in Utility Distribution

Reliability and protection in utility distribution are safeguarded through breakers, relays, automation, and fault isolation, ensuring grid stability, preventing outages, and providing safe, resilient power for residential, commercial, and industrial users.

 

What is Reliability & Protection in Utility Distribution?

Reliability and protection in utility distribution ensure safe, continuous electricity delivery by detecting faults, isolating affected areas, and restoring service efficiently.

✅ Uses relays, reclosers, and breakers to clear faults quickly

✅ Improves outage performance with automation and fault isolation

✅ Adapts to DER integration for stronger grid reliability

Part of enhancing reliability and protection in Utility Distribution involves harmonizing protection strategies with the overall network design, as discussed in our overview of electrical distribution systems.

Utility distribution is where electricity meets the customer, and its reliability depends on strong protection strategies. Faults, equipment failures, and severe weather are inevitable — but with coordinated protection, utilities can minimize outages and restore service quickly. Reliability and protection are not just technical concerns; they define the customer experience and the resilience of the modern grid. One of the key challenges to reliability in utility distribution is dealing with costly interconnection delays, which can slow down system upgrades and impact protection planning.

 

The Role of Protection in Reliability

In utility networks, reliability is measured through indices such as SAIDI, SAIFI, and CAIDI, which track outage frequency and duration. Behind those numbers lies a simple principle: protection devices must respond fast enough to clear faults but selective enough to avoid cutting off more customers than necessary.

Consider a radial feeder serving a rural community. A single fault along the line can interrupt service for everyone downstream. With the right combination of breakers, reclosers, and fuses, that same fault could be confined to a small segment, keeping most customers supplied while crews make repairs.

 

Layers of Protection in Utility Distribution

Protection in utility distribution relies on multiple devices working together:

  • Breakers at substations interrupt large fault currents.

  • Reclosers attempt to clear temporary faults and restore service automatically.

  • Sectionalizers detect passing fault current and open to isolate problem areas.

  • Fuses protect lateral branches and small loads.

The effectiveness of these devices comes from careful coordination. Each must operate in the right sequence so that the smallest possible section is taken out of service. Poor coordination risks unnecessary outages, while proper design ensures reliability. Understanding electric power distribution provides the foundation for evaluating how protection devices interact within the broader utility grid.

 

Comparative Roles of Protection Devices in Utility Distribution

Device Typical Fault Response Time Coverage Area Reliability Impact
Breaker Instant to a few cycles Entire feeder circuit Prevents catastrophic faults from spreading upstream.
Recloser Less than 1 second, with reclosing attempts Feeder segments Clears temporary faults, reducing unnecessary outages.
Sectionalizer Opens after fault current passes Branch or loop section Isolates smaller faulted areas, keeping most customers online.
Fuse Seconds (melts under sustained fault) Small branches, taps Protects localized loads, acts as final safeguard.

 

Effective protection depends on critical components like the electrical insulator, which maintains safety and stability by preventing leakage currents and supporting conductors. To minimize downtime and improve service reliability, utilities often rely on monitoring devices, such as fault indicators, to pinpoint disturbances quickly.

 

Protection Coordination in Action

Protection is effective only when devices operate in harmony. Two common strategies are:

  • Fuse-saving: a recloser operates first, giving temporary faults a chance to clear before a fuse blows.

  • Fuse-blowing: the fuse operates on sustained faults, preventing upstream devices from unnecessarily tripping.

Modern adaptive relays now adjust thresholds dynamically. For example, when distributed energy is producing heavily, relay settings shift to account for reverse power flow.

Did you know? FLISR (Fault Location, Isolation, and Service Restoration) can reconfigure feeders in under 60 seconds. One Midwestern utility reported a 25% reduction in SAIDI after installing automated reclosers and FLISR software across its suburban service territory.

 

Smart Protection and Automation

Utilities are increasingly adopting automated protection schemes. Fault Location, Isolation, and Service Restoration (FLISR) technology uses sensors, communications, and smart switches to reroute power in seconds. Instead of dispatching crews to manually isolate a fault, the system reconfigures itself, reducing both outage duration and the number of affected customers.

 

Automation turns protection from a reactive safeguard into a proactive reliability tool. Utilities that deploy digital relays, SCADA integration, and smart switching see measurable improvements in performance, with lower SAIFI and CAIDI values across their service areas. Advances in distribution automation enable utilities to detect faults, isolate problem areas, and restore service more quickly, directly improving reliability indices such as SAIDI and SAIFI.

 

Impact of Protection and Automation on Reliability Indices

Reliability Index Definition Effect of Protection & Automation
SAIDI Average outage duration per customer (minutes/year) Automation reduces restoration time by rerouting power quickly.
SAIFI Average number of outages per customer (interruptions/year) Coordinated reclosers and sectionalizers lower outage frequency.
CAIDI Average outage duration per interruption Faster fault isolation and service restoration shorten each outage.

 

Challenges in a Distributed Era

Distributed energy resources (DERs) such as solar, wind, and storage are transforming how protection operates. Power no longer flows one way from the substation to the customer. Reverse flows can confuse traditional protection settings, while inverter-based resources may not produce fault currents large enough to trigger older devices. 

To address this, utilities are deploying directional relays, adaptive settings, and advanced digital relays capable of handling bidirectional power. Protection strategies must evolve in tandem with the grid to maintain reliability as more distributed resources connect at the distribution level. The rapid growth of distributed energy resources has reshaped how utilities design protection schemes, necessitating adaptive relays and more sophisticated coordination strategies.

 

Barriers to Stronger Protection

Despite technological progress, several barriers remain:

  • Interoperability between legacy and digital equipment is often limited.

  • Communication networks must be robust enough to support widespread automation.

  • Cybersecurity is critical, as protection devices are now part of utility control systems.

  • Workforce skills must expand, with protection engineers learning networking and analytics alongside relay coordination.

Utilities that overcome these barriers position themselves to deliver safer and more reliable services in the decades ahead. Long-term resilience in distribution systems also depends on strong links with electricity transmission, which supplies the bulk power that distribution networks deliver safely to end users.

Reliability and protection in utility distribution are inseparable. Protection devices detect, isolate, and clear faults; reliability is the result of how well those devices are coordinated. With automation, adaptive relays, and smarter strategies, utilities can minimize outages and keep customers connected even as the grid grows more complex. In an era of distributed resources and rising expectations, robust protection is the foundation of reliable utility distribution.

 

Related Articles

 

View more

Understanding How Overhead Switchgear Innovation Cost-Effectively

How Overhead Switchgear Innovation Cost Effectively? Advanced medium-voltage reclosers, vacuum interrupters, and SCADA-enabled smart sensors enhance reliability, reduce arc-flash risk, cut lifecycle maintenance, and optimize distribution networks for grid modernization and predictive maintenance.

 

How Overhead Switchgear Innovation Cost Effectively?

Deploy SCADA-ready reclosers, vacuum tech, and sensors to boost reliability, cut OPEX, and extend asset life.

✅ Medium-voltage reclosers and sectionalizers lower fault costs

✅ Vacuum interrupters reduce maintenance and minimize arc-flash hazards

✅ SCADA, IoT sensors enable predictive maintenance and uptime

 

BACKGROUND
Achieving many of the globe’s top priorities depends on an unprecedented expansion of electric generation capacity. A report released last year by the Electric Power Research Institute (EPRI), for example, forecast that achieving net-zero carbon emissions in the U.S. by mid-century would require a nearly 500 percent increase in electricity generating capacity.
A decarbonized future powered largely by renewable electricity generation depends on a reliable grid, especially the transmission grid. A new report by the National Academies of Science, Engineering, and Medicine in the U.S. laid out a blueprint for achieving 2050 net-zero goals, and strengthening and expanding the transmission system was a key component because the transmission system is so important both to integrating renewables and delivering clean energy to where it is consumed. The reliability of the transmission and sub-transmission grid is particularly vital as clean electricity is increasingly relied on to fuel transportation, heating and cooling, and manufacturing and industrial processes. Indeed, the ability to sectionalize and reroute power when an outage hits the sub-transmission system has an outsized impact on reliability because high-voltage grids serve so many homes and businesses. As planners modernize regional networks, an understanding of electricity transmission principles helps explain how long-distance power flows and interconnections support resilience.
The high costs and environmental impacts of status quo solutions
G&W Electric’s Viper®-HV overhead switchgear solution is an important innovation in efforts to simultaneously reduce utility operating expenses (OPEX), improve sub-transmission grid reliability, and integrate more renewables. The genesis of the Viper-HV switching solution was when two utilities approached G&W Electric, one of the U.S.’s largest recloser and switchgear manufacturers, with the request that the company develop a 72.5 kV recloser able to switch and sectionalize sub-transmission power lines to maintain reliability. Deployed on critical transmission lines, such devices expand sectionalizing options without the footprint of new substations.
The reason the utilities and the wider industry were so keen on an overhead solid dielectric solution able to enhance sub-transmission grid reliability was because existing options were inadequate – especially because the sub-transmission system needs both the ability to sectionalize the grid to maintain reliability when faults occur and because it demands advanced monitoring to quickly detect, locate, and respond to outages. Historically, sectionalizing the sub-transmission grid has been handled by motor-operated switches that were insulated either by air or gases such as SF6. Because these products are mechanical devices, they require frequent inspection and maintenance. Not only does this put stress on already tight utility OPEX budgets and a workforce stretched thin by retirements, mechanical devices exposed to the elements can also fail. Utilities increasingly pair such equipment with distribution automation strategies to accelerate fault isolation and service restoration.
Overhead switchgear innovation drives desired and unexpected sub-transmission grid benefits
Development of the Viper-HV overhead switchgear solution took years, with significant input from customers and industry experts. But the advances made deliver important benefits to sub-transmission grid reliability and intelligence, along with improved costs. Indeed, the Viper-HV is a solid dielectric overhead switchgear solution that can respond quickly to temporary faults and deliver the sectionalizing the utilities originally requested, as well as serving as a creative alternative to circuit breakers and bringing reclosing capabilities where applicable. These capabilities align with broader smart grid objectives that emphasize pervasive sensing, coordinated control, and adaptive protection.
Manufactured with a robust, proprietary, time-proven process, the Viper-HV solution is made to solve several pressing sub-transmission grid reliability and cost concerns. For example, it is made to complete a minimum of 10,000 operations without any need for maintenance – which delivers relief to utility OPEX budgets and frees up limited staff for other tasks. Reduced maintenance cycles also streamline power distribution workflows and spare-parts planning for field crews.
Besides providing a low-cost, no-maintenance solution for sub-transmission grid sectionalizing, advanced reclosing technology is important for other reasons as well, including:
Precise location of faults for rapid power restoration
One of the primary challenges facing utilities trying to restore power when there is an outage is finding the fault that caused it. Existing solutions can approximate the location of a fault, which still requires utility personnel to devote precious time to pinpointing its exact location – often in harsh weather conditions – which results in longer restoration times and customer and regulator frustration. The Viper-HV overheard switchgear solution can be equipped with controllers with built-in intelligence enabling precise fault location. The Viper-HV solution includes switching technology plus controllers to include not just impedancebased algorithms but traveling wave fault location determination, which is suitable on longer sub-transmission lines. While most sub-transmission applications are AC, awareness of evolving direct current technology informs protection coordination, converter siting, and interoperability decisions.
Rapid and less costly integration of renewables
Many nations are accelerating deployments of renewable energy to reduce greenhouse gas emissions and achieve ambitious decarbonization targets. Distributed energy resources (DERs) like solar and wind increasingly connect to the transmission and sub-transmission grid – especially when an extra transmission line is added to existing infrastructure to take advantage of an advantageous renewable energy location. DERs introduce complexity to the grid, including more frequent switching than is normal on sub-transmission feeders. The Viper-HV technology, since it was certified as a recloser with 10,000 operations capability, is more suitable than traditional motor operated switches. Furthermore, the form factor of the Viper-HV overhead switchgear is easier to install than other solutions. Pairing sectionalizing schemes with strategically sited critical energy storage can further smooth variability and enhance grid stability during switching events.
Removes need to add expensive and time-consuming grid infrastructure
Another significant benefit of advanced overhead switchgear technology: it can avoid the necessity to add new substations. In cases when a new feeder and circuit breaker need to be added to a sub-transmission system substation, the Viper-HV overhead switchgear solution can increase the speed and lower the cost. That’s because traditional circuit breakers need to be ground-mounted on a concrete pad, which takes up space many substations don’t have and involves permitting that can take a lot of time. By contrast, the Viper-HV overhead switchgear solution can be mounted on the already grounded metal frames most substations have available. This takes no additional space and doesn’t require a time-consuming permitting process.
Advances in technology are essential for increasing the reliability and resiliency of the sub-transmission grid. At the same time, these technologies must lower, rather than elevate, the total overall costs including all aspects of the installation and lifecycle costs (i.e. maintenance, replacement). Sophisticated overhead switchgear technology provides a budget-friendly option for enhancing reliability, resiliency, and helping to green the power grid.
 

 

Related Articles

View more

Power Line Carrier Communication Explained

Power line carrier communication enables data transmission over electrical power lines for grid automation, SCADA telemetry, and protective relaying, using coupling capacitors, line traps, and narrowband modulation to support substation monitoring and smart grid control.

 

What Is Power Line Carrier Communication?

A narrowband method sending control, protection, and telemetry data over power lines using coupling and line-trap equipment.

✅ Uses coupling capacitors and line traps to inject and isolate signals

✅ Supports SCADA, teleprotection, and substation automation traffic

✅ Typically narrowband FSK/PSK; robust against high-voltage noise

 

Power line carrier communication (PLCC) is a vital technology for electrical professionals to understand in today's evolving energy landscape. By utilizing existing power lines for data transmission, PLCC offers a cost-effective and reliable communication solution for a wide range of applications within industrial, commercial, and institutional power systems. In transmission engineering contexts, PLCC must account for impedance characteristics of overhead transmission lines to maintain carrier signal integrity across long spans.

Let's explore the evolution of PLCC, its crucial role in smart grids, its advantages compared to alternative communication technologies, the cybersecurity challenges it faces, and its integration with SCADA systems. By understanding these key concepts, we can harness the power of PLCC to enhance the efficiency, reliability, and security of modern power systems. These concepts align closely with the principles outlined in smart grid architectures that emphasize interoperability and resilience.

Power line carrier communication has emerged as a versatile and essential technology in modern industrial, commercial, and institutional power systems. By leveraging existing electrical infrastructure for data transmission, it offers a cost-effective and reliable solution for a wide range of applications. Within utility operations, PLCC complements core power distribution practices by enabling telemetry and control without new cabling.

 

Evolution of PLCC in Power Distribution

Power line carrier communication has come a long way from its early days of simple signaling and control functions. Initially, it relied on narrowband carrier frequencies transmitted over high voltage power lines. To achieve this, systems employed coupling capacitors, which provide high impedance to power frequency while allowing the passage of higher carrier frequencies. This ensures that the carrier signals do not interfere with the power flow. Furthermore, wave traps, also known as line traps, were installed to prevent the carrier signals from propagating beyond the desired sections of the power line, effectively creating a trap line for the communication signals. These early systems, often employing band pass filtering to further isolate carrier signals, were primarily used for basic communication between substations and protective relaying. However, with the rise of smart grids and advanced automation needs, PLCC has evolved to encompass broadband technologies, enabling higher data rates and supporting a wider range of applications. This evolution has been driven by advancements in signal processing, modulation techniques, and the development of sophisticated PLC terminal equipment. Design considerations also differ from direct current technology where coupling, filtering, and insulation coordination require different approaches.


Applications in Smart Grids

Power line carrier communication plays a crucial role in enabling the functionalities of modern smart grids. By providing a communication backbone for various grid devices, PLCC facilitates real-time monitoring and control of the power system. This includes applications like demand response, where it enables dynamic pricing and load control to optimize energy consumption. Moreover, it supports voltage control by allowing for real-time adjustments to maintain grid stability. It also aids in fault location by providing precise information about the location of disturbances, enabling faster restoration of power supply. PLCC can also coordinate distributed energy resources such as rooftop solar and battery inverters for local balancing and protection schemes.

 

PLCC vs. Alternative Communication Technologies

While it offers numerous advantages, it's essential to compare it with other communication technologies used in power distribution. Wireless communication, for instance, offers flexibility and ease of deployment but can be susceptible to interference and may have limited range, potentially impacting signal to noise ratio. Fiber optic communication provides high bandwidth and security but can be expensive to install, especially in challenging terrains. Coaxial cable, while offering a balance between cost and performance, may not be as readily available as existing electrical infrastructure. However, coaxial cables play a critical role within systems themselves, as they are often used to connect the equipment to the coupling capacitors, efficiently carrying the high-frequency carrier signals with minimal loss. PLCC, with its cost-effective utilization of existing power lines, often proves to be a compelling choice, particularly for applications requiring wide coverage and reliable communication in industrial settings. At the feeder level, advancements in overhead switchgear complement PLCC by enabling faster sectionalizing and restoration decisions.

 

Cybersecurity Challenges and Solutions

As power line carrier communication systems become more integrated into critical power infrastructure, ensuring their cybersecurity is paramount. PLCC is vulnerable to cyberattacks that can disrupt operations, compromise data integrity, and even cause widespread power outages. To mitigate these risks, robust security measures are essential. Encryption techniques protect sensitive data transmitted over PLCC channels, while authentication mechanisms prevent unauthorized access to the system. Intrusion detection systems continuously monitor the network for suspicious activity, enabling prompt response to potential threats. By implementing these security solutions, power systems can enhance the resilience of their infrastructure against cyberattacks. As utilities deploy more critical energy storage systems, securing PLCC channels that supervise these assets becomes increasingly important.

 

Integration with SCADA Systems

Power line carrier communication seamlessly integrates with SCADA systems, enhancing their functionality and providing real-time data for grid monitoring and control. SCADA systems rely on communication networks to gather data from remote terminal units (RTUs) and intelligent electronic devices (IEDs) located throughout the power system. It acts as a reliable and efficient communication channel for transmitting this data to the central control center. This real-time information enables operators to monitor grid conditions, detect anomalies, and take corrective actions promptly. The integration with SCADA systems improves situational awareness, facilitates faster response times, and enhances the overall efficiency of power distribution operations. Furthermore, by utilizing PLCC for communication, SCADA systems can leverage the inherent protection offered by devices like protective relays and wave traps, enhancing the overall system reliability.

 

Leading Questions:

What are the core advantages?

Power line carrier communication leverages existing electrical infrastructure, making it cost-effective. It offers wide coverage, especially in remote areas, and the inherent robustness of power lines ensures reliable communication even in harsh environments.

How does it contribute to smart grids?

PLCC enables essential smart grid features like demand response, voltage control, and fault location, contributing to optimized energy consumption, grid stability, and efficient power restoration.

What are the main challenges?

Signal attenuation and noise over long distances, electromagnetic compatibility issues, cybersecurity vulnerabilities, and ensuring interoperability between different PLCC equipment are some of the challenges.

How do narrowband and broadband technologies differ?

Narrowband PLCC typically uses lower carrier frequencies and is suitable for longer distances and applications like SCADA and protection relaying. Broadband PLCC, with its higher data rates, caters to modern applications like smart metering and grid automation.

What are the future trends?

Advanced signal processing techniques, integration with IoT devices, enhanced cybersecurity measures, and applications in electric vehicle charging infrastructure are some of the future trends shaping the evolution of PLCC.

 

Related Articles

View more

Electric Power Distribution

Electric power distribution delivers electricity from substations to homes, businesses, and industries, using transformers, feeders, and circuits to maintain voltage stability, ensure reliability, and support safe, efficient energy delivery.

 

What is Electric Power Distribution?

Electric power distribution transfers medium-voltage electricity—typically ranging from 2 kV to 35 kV—from distribution substations to end users. This voltage is stepped down by distribution transformers to secondary levels, such as 120/240 V in North America, for residential and commercial consumption.

✅ Transfers electricity from generation plants through substations to end users

✅ Uses transformers, feeder lines, and distribution circuits for voltage control

✅ Ensures safe, reliable, and efficient energy delivery

Distribution systems are a subset of the larger grid, linking transmission lines, substations, transformers, and service drops into a cohesive network. Their design must ensure voltage regulation, load balancing, and service continuity, even under fault conditions or peak load demand. Modern electrical distribution systems combine traditional infrastructure with advanced monitoring to ensure safe and efficient energy delivery.

 

Core Components of the Distribution System

Transformers and Voltage Regulation

Transformers adjust voltage levels to match the stage of delivery. High voltages—such as 12.47 kV or 13.8 kV—are optimal for efficient medium-distance transportation through primary feeder circuits. On-load tap-changing (OLTC) transformers automatically regulate output voltage in response to load changes, while capacitor banks correct power factor and help maintain system stability. These devices are essential for ensuring end users receive power at a safe and usable level.

 

Distribution Substations

Distribution substations act as hubs, connecting high-voltage transmission lines to medium-voltage distribution networks. Inside, busbars distribute power to multiple feeders, while circuit breakers, reclosers, and surge arresters protect against short circuits, overloads, and transient overvoltages. Voltage regulators and switching gear allow operators to maintain optimal operating conditions and reroute power as needed.

 

Transmission and Primary Circuits

Transmission lines move energy over long distances at high voltages to minimize energy losses. At the substation, voltages are stepped down for entry into the primary distribution network. Primary circuits—often operating in the medium-voltage range—carry power to local areas, where it will be stepped down again for secondary distribution. The role of electricity transmission is critical in moving high-voltage power from generation plants to substations before it enters the distribution network. Distribution lines connect local communities to the larger power grid, receiving electricity from the high-voltage transmission system and delivering it safely to end users.

 

Distribution Network Designs and Reliability

Distribution networks are typically designed as radial systems or network configurations.

  • Radial feeders resemble a tree structure, with each branch supplying a specific area. They are cost-effective and common in suburban and rural regions but more vulnerable to outages.

  • Network systems interconnect multiple feeders and transformers, allowing energy to flow from several directions. This improves reliability in dense urban areas, where service continuity is critical.

Tie switches connect different feeders, enabling operators to reroute power during maintenance or outages without prolonged service interruptions.

 

Modern Advancements in Distribution

Smart Grid Technology

The smart grid integrates advanced monitoring, automation, and communication systems into traditional power distribution. Supervisory Control and Data Acquisition (SCADA) platforms collect real-time performance data, while automated reclosers and remote-controlled switches enable rapid fault isolation and service restoration. By improving visibility and control, smart grids enhance efficiency, reduce downtime, and optimize voltage profiles. Utilities are increasingly adopting distribution automation technologies to improve reliability, reduce outage times, and optimize network performance.

 

Distributed Generation and Renewables

Today’s distribution systems increasingly accommodate distributed energy resources (DERs) such as rooftop solar panels, wind turbines, and battery storage. Microgrids allow localized energy generation and storage, supporting grid resilience during disturbances. This integration demands bidirectional power flow management, voltage regulation strategies, and advanced protection schemes. The integration of distributed energy resources such as solar, wind, and battery storage is reshaping how power is generated and delivered at the distribution level.

 

Operational Strategies for Efficiency and Safety

Load Management

Load management is the practice of balancing electricity supply and demand in real time. Utilities employ demand response programs to reduce peak loads, shift consumption to off-peak hours, and avoid overloading critical equipment. Energy storage systems, such as lithium-ion batteries, supplement supply during high-demand periods and store excess energy when demand is low.

 

Voltage Regulation and Protection Systems

Maintaining voltage within acceptable limits is essential for both equipment longevity and service quality. Utilities use OLTC transformers, capacitor banks, and line voltage regulators to ensure consistent voltage delivery. Protective equipment—circuit breakers, fuses, reclosers, and surge arresters—safeguards against equipment damage, electrical faults, and safety hazards. SCADA integration allows real-time monitoring and swift corrective action.

 

Feeder Circuits and Switches

Feeder circuits, whether overhead or underground, carry medium-voltage electricity from substations to distribution transformers. Sectionalizing switches allow operators to isolate parts of the feeder for maintenance, improve load balancing, and quickly restore service after a fault. Deploying a fault indicator along feeder lines allows utilities to quickly pinpoint and isolate problems, reducing downtime and maintenance costs.

 

Final Stage: Delivery to the End User

At the final step, distribution transformers—mounted on utility poles, in pad-mounted cabinets, or installed in underground vaults—reduce medium-voltage power to secondary voltages suitable for end-user applications. Residential customers typically receive 120/240 V service, while commercial and industrial users may require higher secondary voltages. This last transformation ensures safe, reliable, and efficient power delivery tailored to the specific needs of each customer.

 